Think the only way out of this information impasse is to approach manufacturers and ask for the max fault current that their RCD's and RCCBO's will withstand WITHIN STATED RCD OPERATION TIMES i.e. mS.
I suspect in many cases these withstand currents will be less than the earth fault loop impedance will let through in the event of an earth fault .
Then one relies on the MCB part of the RCCBO or a Fuse to break the fault current at much longer operating times and ELZ becomes highly important.
It is not unknown for max withstand current for RCD to be say 200 amps and min operating current for MCB to be 300 amps (30 amp type C MCB) ELZ 0.64ohms is imperative.
Regards Mijo