Just to clarify this is a home project for a small home business.
No dont worry about it

criticism is what i am here for.
Im looking into the semiconductor fuse for the relay but have never seen them used before.
Do you have any external control devices remote from the panel... if so what control voltage have you implemented? (Can you explain further please)
The pid, lights, fan and entire circuit will be fused. Ye there will be a neutral just got sloppy with the diagram.
Only picked up switches, fusses, Fuse holders and common connection blocks.
Picked up these common blocks just for you FAA Greenie, no more chocky blocks. They will be used for ground, live and neutral.
Phil- ye getting this wire but not ordered yet, what do you think?
heat resistant 2.5mm fibreglass wire per meter appliance cable high temp spares | eBay
So that would be 40 amp breaker 25 amp wire and 100A common blocks. Any better? Total draw from elements,lights,fan and pid= 35.5A
10A switch for lights (2A circuit) and 5A fuse
10A switch for pid (0.09A draw) and 1A fuse from builders instruction.
Got 15A switches for the elements (10.4A)
Keep the criticism up.
Really grateful