Discuss Wiring new hob in the Industrial Electricians' Talk area at ElectriciansForums.net
1hammer
I bought a new hotpoint electric hob which says it must be wired to a junction box with 6mm cable.
Why should it be wired into a junction box before connecting it to the 45A cooker circuit instead of running the cable direct from the hob to cooker switch?
I think they mean a cooker connection unit which is normally after the switch lower down the wall so cable can not be seen when connected.
Thanks Ian - so the cable can be run straight from the hob to the switched ccu (no additional junction box) ?
The oven has a low wattage so will be fitted with 13A plug and put straight into the wall socket
You will need to fit a cooker oulet below, your 6mm will be connected to this from your cooker switch. then a length of 6mm from the cooker to the outlet.
Hammer. The installation instruction should tell you that you have to use a special heat resistant cable for the final connection to the hob.
Fred
Not sure if I've got the wrong end of the stick (probably!) but 6mm on a 45A circuit? Thats pushing it a bit isn't it? With regards to heat resistance I've never seen this in instructions ( but then rarely read them!) A cooker hob etc should be so insulated to keep heat where it's required, but I've been wrong before (many times)
Hi mate , you can connect the hob straight into the 45 amp switch if you have no cooker outlet ( the out lets are normally below work surface height) , you may have one and not spotted it
>>>Marbo 45A DP Cooker Connection Unit - NoLinkingToThis, Where the Trade Buys
as far putting your hob on a plug top >> double check your instruction as elecy hobs normally pull a higher load than 13amps , and will need to be hard wired into the back of your 45amp switch .
HTH
Well that what it said in the Hotpoint Manual.Special cable conforming to type H05BB-F Tmax 90; or higher.Maximum load of 6.4 kW.Here is an interesting part,"The Hob may only be installed over drawers when a fire -proof shield has been fitted to the lower part of the unit"
Better still, install CCU c/w 13amp socket in adjacent cupboard. Wire hob directly from CCU and plug oven into socket.
No need for heat resisting cable. Use standard 6mm T&E as hob is usually around 6kW (24amps).
24amps for hob, 12 amps for oven - 40amp MCB
J/Spark. So in your opinion Hotpoint and all Hob manufactures do not know what they are talking about when they specify a special cable to be used.You are offering bad and dangerous advice.
You should be ashamed of yourself.
Slightly unrelated but this has interested me for some time as I am seeing it more and more.
1 The "hob" is the bit on top and on checking Hotpoint's website could draw up to 7.2 kW.
2 The bit below the worktop is an oven and very often is supplied with a fitted 13amp plug.
3 A cooker is usually a stand alone appliance, hob & oven as one unit and if all electric is supplied by a single cable and on average could draw around 11kW.
This is the bit that tickles me. When hob and oven are installed as seperate units the hob quite rightly is connected to the cooker point while the oven is pluged into the nearest below worktop socket (think granite worktops). Come the day that the oven contacts weld together and the joint is in flames inside it, where do you turn the damn thing off! Comments from those in the testing and inspecting world would be most appreciated.
Ps I must add that the above is not a practice I follow myself but have had to deal with twice now.
Bits I'm not sure about; what size breaker on the 6mm between breaker and CCU? Can Isolater switches be hidden in cupboards? I don't use HR cable when connecting outlet to cooker as i tend to fit cookers into pretty flammable cupboards. maybe the hob manufacturers are covering their ar5es
Spark. Only forty years?So you are still a boy yet.You might have had no problems but you can not possible tell if some of your early work has not gone up in smoke by now.
We are talking about a modern ceramic hob here,times have changed since every kitchen in the land had a Belling.
I can not see the problem in using the correct cable.XLPE cable is not that expensive,easy to get and little bit easy to handle.That extra 20 degrees of protection could be vital in preventing a hydrogen chloride blacked-out kitchen.
As for Jeremy he admits he never reads installation instructions.so he does not have a clue as to what cable to us.Then comes up with same lame excuse about the hob not being installed in a combustible area.What rubbish!Perhaps he does not realize that the radiated heat from around the hob is the reason for fitting HR cable.
There are a few references on this forum about appearing before the beak for one reason or another.You should think about this the next time when you can't really be bothered to do the job properly.
Reply to Wiring new hob in the Industrial Electricians' Talk area at ElectriciansForums.net
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if...
