I have a problem with a toilet light fitting. I have attached a picture of the wiring in the ceiling. This is exactly how it was when I looked at it. The cable with the black and red coming from is the live feed. So the cable with the red and blue wires should be the switch cable. The problem I have is that the cable from the string pull switch is red and black. I cannot get a circuit with the blue and red cable. If I connect the two reds in the block I get a short.

Any help appreciated.
 

Attachments

  • Wiring problem forforum - EletriciansForums.net
    forforum.jpg
    23.8 KB · Views: 91
Best way to check which one is the switch wire is to switch off the supply and use a continuity tester and voltage indicator of some sort to establish exactly whats what.

Edit
Sorry just re read your post.

Is the yellow definatley an earth?
 
Last edited by a moderator:
Possibly a J/B somewhere.Sounds like it may have been added or extended at some point.Is there a fan connected to this as well.Looked like a fan in the corner of the picture
 
Last edited by a moderator:
Hi yer Richtrucker,

Here are my thoughts based on your picture...

It looks like you have a 2-core & cpc ...plus a 3-core & cpc

The two cpcs appear to be twisted and enclosed in the same g/y sleeving
The yellow of the 3-core& cpc appears to be connected to the cpcs.
Could it be that this 3-core & cpc feeds the adjacent fan and when you connect the 2 reds together you are effectively causing a short through the fan, as this yellow wire will become live via the timer fan electronics circuit and you have the other end connected to the cpcs .....does this seem a possibility?
You could have the cable from the pull switch popped up into the ceiling out of sight



spark1 :(
 
i think spark1 is on the right track i just wonder why a 3c was taken to the fan as there is no perm live at the light
unless the 3c is the feed in and the twin goes to the fan and its via a humidi stat
so 3c red to twin red blue to black neutral to light and switch wire yellow to light
 
Is there a isolator for the fan, that is fed permanent. Just a thought.
 

Reply to Wiring problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock