Hi
I am new on here, I have recently had a new Vaillant eco tec 424 plus boiler replacing my old knackered Ideal Classic. It was installed by an advanced Vaillant engineer. It is a Y plan system and the problem is that although it works when the programmer is calling for heat or water it works fine, but when the programmer timer finishes the pump goes off but the boiler does not switch off. It continues to fire up and cool down continuously and the radiators upstairs stay warm, eventually the boiler goes into fault 83 mode and switches the boiler off. I had a Vaillant engineer come and look at it and he tells me that it as not been wired correctly as no pump override wire as been installed. The installer says that he as wired it correctly. Therefore does anyone on here have a Y plan for this boiler so that I can check who is right before i blow my top. The new programmer is a Honeywell ST9420C and the room stat is a wireless Honeywell DT92E. I would be most grateful for advice.
Thankyou
 
Hi Mick and welcome , I have pre approved your post to try and get you some answers, but Admin may move it to the Diy section when they are next online.
 
A standard Y plan with pump over run. Instead of the pump connecting up with the orange of the valve and normally closed of the cylinder thermostat it should be connected to the pump terminal in the boiler.
 

Reply to Y plan for Vaillant eco tec 424 plus boiler in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

A
  • Article
Problem with Vaillant eco tec boiler My 10 year old Vaillant Eco Tec Boiler pump/fan occasionally turns on for 10 secs when the cold water supply...
Replies
0
Views
113
alanem
A
D
  • Article
W-plan pump run on Son recently moved into a 20 year old house with what appears to be a W-plan system using, I think a Worcester Bosch Greenstar...
Replies
0
Views
133
davidwf
D
I was thinking that when the new two port opens and turns boiler and pump on, the normally open port (priority) on the three port is uncontrolled.
Replies
12
Views
2K
Does this help, note com is out not in I have a extended version using this basic system.
Replies
9
Views
2K
Assuming I've been looking at the correct boiler manual 🤔 and your Grundfoss pump external to the bolier is wired to the boiler connector (X16)...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks