Would you also make a Connection to the DNO cable before the cutout or Meter?

Your missing my point or maybe I didn't say it right, what I am saying is as an electrician if that was MY house and there was the chance that with a socket so close there could be a difference in potential then yes I would absolutely bond it if my test proved that it needed bonding. I am not talking about tampering with gas supplies am I, I am talking about attaching a clamp to the exterior pipe! Where is the problem.
 
Would you also make a Connection to the DNO cable before the cutout or Meter?


What's the relevance here, to main bonding an extraneous gas pipe??

But yes, if the incoming cable was a PILC, and the Ze proved suitable by testing, i'd have no problem taking a main earth connection from that cable with a suitable clamp. I wouldn't however make a DIY N-E PME connection....
 
What's the relevance here, to main bonding an extraneous gas pipe??

But yes, if the incoming cable was a PILC, and the Ze proved suitable by testing, i'd have no problem taking a main earth connection from that cable with a suitable clamp. I wouldn't however make a DIY N-E PME connection....

Thank you Eng, it was a flippant comment about the cutout, and totally irrelevant to bonding.
 
Popping out for half an hour to find an headless gas pipe to bond, and get our lass a birthday card brb
 
If there's no Gas meter, You cannot bound to something that's not there.
The gas main is outside the property. So just leave a 10:00mm CPC there for future connection.

Are you for real?? So it doesn't matter to your mind, that the pipe entering the property is extraneous, just that it doesn't have a meter attached to it!! ....Jesus!!

Oh and it WILL be extraneous, on that i'd put money on!! lol!!
 
If there's no Gas meter, You cannot bound to something that's not there.
The gas main is outside the property. So just leave a 10:00mm CPC there for future connection.
I am requoting myself for the benefit of those who only want to read what they want too.

Where abouts is the supply side if a structural steel, ducting etc, all of them could well have to be bonded too if needed.
 
is the gas pipe inside the building or outside? if the latter, it could be argued that it is not extraneous as it does not introduce a potential inside the structure.
 
FFS. For those who seem to have trouble reading English -


544.1.2 states:

The MEB connection to any gas, ... service shall be made as near as practicable to the point of entry...

Where there is ... a meter ... etc.


There isn't a ******* meter so point of entry.


How simple is it?
 
dont waste your time eng mate...

it aint getting through....lol..

I thought trying to win an argument with our lass was hard work but ffs
 
...Oooh,missed a right pedant-fest here...personally,i would induction weld a SS M10 stud on it for a 25mm eye cleat....just in case...
 
Flipping heck, 11 pages over a blooming gas pipe I just wanted a pointeras how best to remove the sodding paint or add pipe to top etc, my god....

oh oh it's inside by the way.

Then bond the bloody thing and be done with it. :32:
 
I am going to bond the pipe, it's you lot who are making a meal out of it!

Oh shut up thee thy started it 125 bloody post's back :sifone:
 
Jesus Christ!!

I work on a large detox wing in a female prison... screaming, shouting, scratching, spitting, moaning.........

And you lot are worse!!!!! :crazy:
 
just be careful with that BS951. you could crush the pipe. :martini_shaken::yesnod:
 
just to digrees from a boring gas pipe. last week was nosing on a site in turkey. new 6 storey hotel. all the usual signs at the site entrance, but not a hard hat to be seen, every worker in trainers, the only thing hi-vis was bald heads under a hot sun. scaffolding climbed with not a ladder to be seen.

in the local hospital there were no crushed skulls, no flattened feet, nobody impaled on the forks of a stacker truck, in fact, nothing to laugh at at all. makes you wonder.
 
yep. thank allah ( oops). just on my 3rd old peculier. stomach is slowly returning to normal and gas is escaping from orifices.
 
Is it gas pipe or is it a pipe with gas in it, would gas bored just leave a supply to house with no meter think about it you can just con up and all your heating will be free , think they would cut of in street, ring them up and ask, or just take paint off pipe with something and bond then test all good at end day, you can go home put feet up and what for next job
 
Could just briefly turn the valve on to see if it is actually connected to mains gas. Daz
 
Be assured it very probably will be, but I have to ask what would the presence - or not - of gas in the pipe have to do with the issue of does it need bonding?? :dead:

Was just replying to post 143 about the availability of free un metered gas. Daz
 
Think it's to do with it's a pipe, you can not see what's in in but you think something is in it, so your mind start thinking what's in in, then you think s..t it's a gas pipe and I do want to touch it, but if it was a water pipe you would just get the sharpes thing out tool box get the paint of and bound it test go home have dinner, beer go to bed
 
Just turn the valve on about a third of the way. Daz

Which will reduce the flow but not the pressure. Nor will it regulate the pressure to keep it constant. That is the job of the governor.

By all means try it and see what happens ...... I'll send flowers to your funeral. ;)
 

Reply to Your thoughts on bonding this gas pipe in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a large gym in the garden and it gets ridiculously hot in the summer. I have utilised pretty much every inch of space and do not want to...
Replies
23
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
978
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
1K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
751

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock