Hi. I’ve just tested a friends DB and it recorded a Ze of 0.50 ohms on a TN-C-S with an 80amp fuse is this ok. As the DNO state that the 0.35 ohms is for 100 amp..
 
Out of interest if the dno does say it’s ok what’s his next move? Obviously he can’t work on the installation and record a Ze within what’s acceptable,still learning so these things keep me awake at night......
 
Last edited:
Out of interest if the dno does say it’s ok what’s his next move? Obviously he can’t work on the installation and recited a Ze within what’s acceptable,still learning so these things keep me awake at night......
If all his Zs reads are within parameters he potentially can. Let's be honest in domestic the R1 +R2 is so low the Zs is normally way under the permissible.
However I would make a note on cert DNO informed with name of person who ok'ed it.
 
They'll probably get you to take the Ze at the cutout to eliminate the possibility of any consumer's equipment (eg tails) causing the problem.
If they OK it get a reference number and quote that on the cert.
 
Out of interest if the dno does say it’s ok what’s his next move? Obviously he can’t work on the installation and record a Ze within what’s acceptable,still learning so these things keep me awake at night......

Regardless of what the DNO say he records the measured Ze on the certificate, and if everything else complies then no problem.
The figure of 0.35 is a guideline typical value, not a fixed maximum permissible value.
As long as the Ze of 0.50 is stable and all circuits comply for Zs then it is fine.
 
Thanks Dave all advice appreciated,read through the link westward put up,explains a lot to a novice,
 
Regardless of what the DNO say he records the measured Ze on the certificate, and if everything else complies then no problem.
The figure of 0.35 is a guideline typical value, not a fixed maximum permissible value.
As long as the Ze of 0.50 is stable and all circuits comply for Zs then it is fine.
Apparently 0.35 ohms is the typical maximum.
 
It is the typical figure for a 100A supply, other supplies will differ.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Thread statistics

Created
Mikeatkinson,
Last reply from
Strima,
Replies
15
Views
3,608

Advert

Back
Top