When measuring Zs values, does everyone apply the correction factors for temperature during fault conditions to the value?
 
I generally use the 80% figures unless the reading is of the higher end of the figures
 
the max. figure is, IMO, that given in BS7671., not some guesstimate of 0.8x because of a non-specified guessed temperature the cable might be at.
 
no u times the regs values by 0.8 and the ones in the OSG have already been corrected
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fine
 
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fine

my thoughts exactly
 
0.8 and 80% are the same thing surely? I meant i would measure zs of a circuit, take the maximum value and if its below the osg value then great there's room for manouver but of course the maximum values are in the bgb so as long as its below that its fine

Those figures are for the Designer. The Inspector should ensure that the measured value does not exceed the corrected value.
 
Those figures are for the Designer. The Inspector should ensure that the measured value does not exceed the corrected value.
Read what i've written! I've said its great if they're below the 80% but fine if they're below the bgb values!
 
If the circuit has already been energised, and has been at full operating temp, then you can use the max values in BS7671.
for an initial verification you should apply the rule of thumb (x 0.8) this is to allow for the increase of resistance as the circuit warms up.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Zs adjustment
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
28

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
KAS1,
Last reply from
monkeyelectric,
Replies
28
Views
3,550

Advert

Back
Top