Robbo

-
Reaction score
1
Doing some prior tests befor installing a fused spur from a radial circuit, and have found the Zs reading higher then the current regs, obviously it complys with a past reg, but as I’ll be doing a minor works for the job, when filling out their cert would I just put it down as an observation in comments on current installation and grade it C3.

Cheers.
 
Personally, no.

The Zs of your install must meet current regs.

This cannot be achieved, without additional works, if the current Zs doesn't comply.

Is the current Zs measured, calculated or from a previous cert?

How many points are on the circuit you're adding to, tightening all terminals could get you down to the Zs you require.
 
Thought not, should just mention as an observation then. Yes thought about changing the RCBO, only it won’t have been quoted for by the company I work for as we don’t do major electrical work, I’m just fitting a spur for a stairlift charger, carry out testing and fill in minor works.

Cheers
 
Just though, could it be argued that the Zs you're interested in is that relating to the fuse in the FCU, which for a 13A BS1362 is 1.8ohms for a 0.4 second disconnection time..
 
There is only a single double socket on the circuit, I’m just adding a fues spur to it on other side of lading, it’s fairly long run to be honest 10-15 mtr of top of my head.
 
What is the Zs reading you're getting?

Also what is the type, rating and make/model of the protective device?
 

Reply to Zs reading does not meet current regs in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock