...There's your issue!Yes it’s a 30mA bs 61009 type C RCBO.
You need to change it to a B type
Just though, could it be argued that the Zs you're interested in is that relating to the fuse in the FCU, which for a 13A BS1362 is 1.8ohms for a 0.4 second disconnection time..
Reading is 0.79 at the furthest point, like I said it’s the only socket on the circuit, and is about 10-15mtr run from its DB
That's why I like this game, and this forum.Well I go to the bottom of our stairs. I got disagrees before, on saying the exact opposite of what GBDamo is saying and getting dumb for here.
Well I go to the bottom of our stairs. I got disagrees before, on saying the exact opposite of what GBDamo is saying and getting dumb for here.

What about fault protection up to the spur.
Ooh, you're so 17th Alan!Earth fault disconnection times are met by the RCD, no requirement to change to a type B unless you want to waste your's or your customers money.
411.4.4 note 2 applies and 411.4.5