Morning, just checking a lighting circuit on a house, I have the main earth disconnected and still get a zs reading of 2.2 ohms. No evidence of an earth spike and bonding goes direct to henley block.

Any suggestions why this could happen??
 
pics. would help. is you 2.2.ohms a reading from the bonding?
 
Parallel path via CPC to boiler circuit CPC to boiler manifold to pipework within the fabric of the building?

Also why is the installation energised with the main earth disconnected?
 
I don't understand either. And why would you expect the CPC to be insulated from earth throughout the installation? It could take any value from infinity to zero without indicating anything abnormal. I can see why it might be useful to know for forensic analysis but not for normal testing.
 
If you have main earth disconnected , surely it would be ZE not ZS.? (at source)

He says he's checking a lighting circuit though, not at the source.
 
So to answer why I had the circuit energised with the main earthing disconnected..

The lighting circuit connected in board had no CPC so I checked the Zs at a ceiling rose.

I had a reading of 2.2 ohms so I then tried to find out where the earth was coming from.

I disconnected all the CPC's from the other circuit in the board, checked Zs again and still had 2.2 ohms.

Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.
 
Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
 
Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
You can’t make an omelette without breaking a few eggs.....
 
Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.

Why do this as a live test when that means doing something as stupid as energising the installation with the earthing conductor disconnected?

Electricians are supposed to understand the fundamental principles of electrical safety!
 

Reply to Zs reading with main earth disconnected in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock