is this a question or a statement
parallel paths, lower ze than max value and temp at time of test?
1. parallel paths
2. meter tolerances
3. temperature variation at time of test
4. probe connections
5. nulling of leads
Reply to Zs readings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net