Zs=Ze+R1+R2 if you have R1+R2 and the Ze of cu through dead testing what is the need of doing an earth fault loop impedance test once you've energised the cu?
Discuss Zs,Ze,R1+R2 in the UK Electrical Forum area at ElectriciansForums.net
Ok so along as you have Ze of cu and R1+R2 no need for earth loop? As you can work out Zs
Ze of cu?Yes but I've got a feeling this could be a long thread. That's 101 of testing.
And I'll correct myself. 'R2'
Zs=Ze+R1+R2 if you have R1+R2 and the Ze of cu through dead testing what is the need of doing an earth fault loop impedance test once you've energised the cu?
...Which is a handy thing,if it is going to be spending most of it's life,in that state.It would confirm that the circuit is now live.....
BS7671 guide for Minor Works has performing the earth fault loop impedance test listed under Part3 : Essential TestsOk so along as you have Ze of cu and R1+R2 no need for earth loop? As you can work out Zs