Hi guys,
been to a fault today where customer is saying they have no power to 6 sockets but all other points ok (all power on one ring main)
when I arrived I checked for power with my martindale and got a L-E reverse symbol at the six points. I then checked voltage at the sockets and got 230v L-E and N-E but nothing L-N. So I thought I must have a neutral fault somewhere.
i then checked ring continuity and found the neutral open circuit. Why would it show voltage across my neutral to earth when all loads have being disconnected. I have checked all sockets and cannot find a loose connection. Any advice on where to go next. If you have any questions where I have not made myself clear just ask. Thanks
 
1. socket testers do give L-E reverse if the N is missing.

2. you will get 230V N-E on the N conductors that are connected through loads to L supply. because the N return to the CU is broken, there's no current flow, therefore no volt drop.
 
draw the house layout on a piece of paper, mark where the sockets are, measure continuity using wander lead, figure how its been wired up, it maybe not a ring anymore. i would suspect a dodgy junction box under the floor.
 
There is still continuity across live and earth, I just found it strange that I was getting voltage across neutral to earth with no loads connected. I have just put everything back together and all sockets have come on with correct voltage but still no continuity,yet when I connect one leg of the neutral the six sockets go back to L-N reverse and then connect the other neutral the rest of the house goes into L-N reverse. Sorry if I'm sounding confusing but Am I basically looking for a break in the neutral that would cause this. Never came across this kind of fault so ur experience is appreciated.
 
I had a problem similar to this, everything looked ok until I attempted to connect a load.
I found that the neutral had been connected in the RCBO but wasn't making contact. It happens with certain breaker terminals
 
It will give you a chance to prove polarity on each socket. Also find out of there are any spurs which may be causing the issue.
 
Yea I'm back there tomorrow so need to get abit more in depth with the testing. Can tell it's not gonna be an easy fault to find seeing as I've checked all accessories so there must be a jb under the floor where the neutral has come loose.
 
Hi guys,
been to a fault today where customer is saying they have no power to 6 sockets but all other points ok (all power on one ring main)
when I arrived I checked for power with my martindale and got a L-E reverse symbol at the six points. I then checked voltage at the sockets and got 230v L-E and N-E but nothing L-N. So I thought I must have a neutral fault somewhere.
i then checked ring continuity and found the neutral open circuit. Why would it show voltage across my neutral to earth when all loads have being disconnected. I have checked all sockets and cannot find a loose connection. Any advice on where to go next. If you have any questions where I have not made myself clear just ask. Thanks
Cut the nonsence regarding continuity checks and whack 500 volts between all cores as you were trained on site and at tech when you did your apprenticeship, it is the only way to check all is okay, 1000 even, any problems will show straight up.
 
any plumbing been done recently? i ask because the other week i had the same fault. the wet-pants had put his circular saw through a 2.5mm. cut clean through the neutral. sod must have known he'd done it as his saw would have stopped. bugger fitted his pipes, nailed the boards back, said nowt. lucky i was in a good mood that day or i'd have nailed his pipes.
 