S
surreysparks
Hi all.
quick question, on a rfc wires in 2.5 single or tne, can you use high integrity sockets and terminate each cpc into a different terminal, and same at the db, or do you have to pull a 4mm radial cpc
in aswell.
i learnt that you could just split the cpc at college years ago, but reading up it apparently needs to be 4mm?
also what would you code a computer circuit with no high integrity earthing on a eicr?
Hi all.
in aswell.
Is the protective conductor current likely to exceed 10ma?
Figure 7.5.3 ON site guide mate. One terminal to be used for each protective conductor including at the DB (obviously a Ring final). The CPC must have a minimum csa of 1.5mm with the circuits marked at the DB indicating high protective conductor currents.
Cheers everyone. But thought it would be more than a c3, as a disconnected cpc could lead to the cpc having half the potential of nominal voltage?
IN my low voltage box along with me new hdmi tester ;) I appreciate what you are hinting at though.
Hi all.
in aswell.
I will need to have one of my rare visits to that good book to see if I am about to state a load of bull
The total area of all the conductors in a multi core cable inc the live conductors shall be not less than 10mm
If that is correct then there will be no code for a twin+E ring final even if its used without the sepearate 4mm earth as per a radial
That depends entirely on what the earth leakage is, just because there are computers on the circuit it doesn't necessarily mean that there will be high cpc current.
surreysparks,
Pete999,