Discuss High integrity earthing in the UK Electrical Forum area at ElectriciansForums.net
S
surreysparks
Hi all.
quick question, on a rfc wires in 2.5 single or tne, can you use high integrity sockets and terminate each cpc into a different terminal, and same at the db, or do you have to pull a 4mm radial cpc
in aswell.
i learnt that you could just split the cpc at college years ago, but reading up it apparently needs to be 4mm?
also what would you code a computer circuit with no high integrity earthing on a eicr?
Hi all.
in aswell.
Is the protective conductor current likely to exceed 10ma?
Figure 7.5.3 ON site guide mate. One terminal to be used for each protective conductor including at the DB (obviously a Ring final). The CPC must have a minimum csa of 1.5mm with the circuits marked at the DB indicating high protective conductor currents.
Cheers everyone. But thought it would be more than a c3, as a disconnected cpc could lead to the cpc having half the potential of nominal voltage?
Hi all.
in aswell.
I will need to have one of my rare visits to that good book to see if I am about to state a load of bull
The total area of all the conductors in a multi core cable inc the live conductors shall be not less than 10mm
If that is correct then there will be no code for a twin+E ring final even if its used without the sepearate 4mm earth as per a radial
Reply to High integrity earthing in the UK Electrical Forum area at ElectriciansForums.net
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Hi All Seen this on a few jobs now where they have on the Downlight fittings where the CPC is terminated outside the enclosure of the Downlight...
5K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...