surreysparks

Hi all.

quick question, on a rfc wires in 2.5 single or tne, can you use high integrity sockets and terminate each cpc into a different terminal, and same at the db, or do you have to pull a 4mm radial cpc
in aswell.

i learnt that you could just split the cpc at college years ago, but reading up it apparently needs to be 4mm?

also what would you code a computer circuit with no high integrity earthing on a eicr?
 
Hi all.

quick question, on a rfc wires in 2.5 single or tne, can you use high integrity sockets and terminate each cpc into a different terminal, and same at the db, or do you have to pull a 4mm radial cpc
in aswell.

i learnt that you could just split the cpc at college years ago, but reading up it apparently needs to be 4mm?

also what would you code a computer circuit with no high integrity earthing on a eicr?

Is the protective conductor current likely to exceed 10ma?
 
Figure 7.5.3 ON site guide mate. One terminal to be used for each protective conductor including at the DB (obviously a Ring final). The CPC must have a minimum csa of 1.5mm with the circuits marked at the DB indicating high protective conductor currents.
 
Hi all.

quick question, on a rfc wires in 2.5 single or tne, can you use high integrity sockets and terminate each cpc into a different terminal, and same at the db, or do you have to pull a 4mm radial cpc
in aswell.

i learnt that you could just split the cpc at college years ago, but reading up it apparently needs to be 4mm?

also what would you code a computer circuit with no high integrity earthing on a eicr?

I will need to have one of my rare visits to that good book to see if I am about to state a load of bull

The total area of all the conductors in a multi core cable inc the live conductors shall be not less than 10mm

If that is correct then there will be no code for a twin+E ring final even if its used without the sepearate 4mm earth as per a radial
 

Reply to High integrity earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Still, if integrity matters you really want two CPC attachment points. In some cases the 2nd CPC might be conduit, etc, so connected separately...
Replies
9
Views
2K
  • Question
With regards to the plastic Hager board made in 2012 you really think I’m going to dismantle the board, order new RCBO’s, and wire it in ? I...
Replies
17
Views
4K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
  • Question
4 months? You think the job is still ongoing? 😀
Replies
18
Views
6K
The safest way to leave the end of a dead cable is to strip back 30mm of insulation off of each conductor and then twist it all together with the...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks