imagejpeg
No diagram
Sorry this is CONTINUITY NOT POLARITY.
Not sure if my tester can do polarity test. It's a fluke 1651b
To test polarity on your dead test. Do the normal test them switch off And then sees what happens when you try the test again
Hi guys and girls. Got a problem on a lighting circuit.
The circuit has a junction box which I have just labeled up.
Theres only 5 lights
OUTSIDE LIGHT x2
SIDE LIGHTS x4
MAIN LIGHT
BEDROOM LIGHT x2
the main light and side lights work the problem is the rest on the light none of them switch.
A volt test shows 240v at the switches with them in both positions.
IR test shows >500 on my fluke
continuity shows fine
earthing is ok.
Anything you you need extra please ask. I'm stumped on this one. I know it's going to be something simple.
You mean 9 lights?
5 lights the x2 and x4 are lights wired in series. Sorry should have been clearer. There is only 5 switch lives in the junction box.
Someone will pull you up on your comment about the lights being wired in series. I assume you know why. I am not nitpicking here by the way, it could be an important point. Daz.
Ldm Are you saying all the lights were working b4 you began, then you’ve installed some LEDs now most of he lights don’t work ?
When you did your continuity test did you try R1+RN as well as you may have a neutral thats not connected correctly and when doing continuity R1+R2 switch the switches on and off then you will know if you have correct polarity this is known as a Dead polarity test. Or remake all connections in the junction box
No. The only 2 lights that worked were the main light and side lights. I can get the others working by swapping the switched live. Not an ideal test I know but proved they can all work. So I know cables are all fine at least they can finish the build. It's got to be a connection either in the junction box or the switches. Most likely junction box...... But where to start.