Do RCDs nuisance trip without an earth fault or is a tripping RCD always the sign of an earth fault?
Not always it could also be that there is a neutral earth reversed somewhere in the circuit if it's a new circuit.
If it is on a board change it could be either a borrowed neutral or on a split board you have connected the wrong neutral in the wrong bar.
If it is a fault on a circuit then it could be an appliance, or a trapped cable or indeed as you say a fault, testing will sort that out
Is this a domestic installation.
Have you ramped tested the RCD?
Only if the appliance has a fault presentOk, what threw me off was the occasional, random tripping. So this is indeed a current imbalance that needs to be traced.
Is it normal for appliances to trip them?
No, not normal but also not necessarily a fault, could be bad circuit design. The earth (CPC) is functional as well as protective.Ok, what threw me off was the occasional, random tripping. So this is indeed a current imbalance that needs to be traced.
I take it you mean low insulation reading.But if the RCD is wired correctly (no faults and high insulation readings), they do not nuisance trip, correct? Tripping always equals earth fault?
Just double checking.
Are you an Electrician? do you understand how an RCD works? if not and I am being kind- should you be working on circuitry? no offence.Do RCDs nuisance trip without an earth fault or is a tripping RCD always the sign of an earth fault?