Do RCDs nuisance trip without an earth fault or is a tripping RCD always the sign of an earth fault?
 
Not always it could also be that there is a neutral earth reversed somewhere in the circuit if it's a new circuit.

If it is on a board change it could be either a borrowed neutral or on a split board you have connected the wrong neutral in the wrong bar.

If it is a fault on a circuit then it could be an appliance, or a trapped cable or indeed as you say a fault, testing will sort that out
 
Not always it could also be that there is a neutral earth reversed somewhere in the circuit if it's a new circuit.

If it is on a board change it could be either a borrowed neutral or on a split board you have connected the wrong neutral in the wrong bar.

If it is a fault on a circuit then it could be an appliance, or a trapped cable or indeed as you say a fault, testing will sort that out


But if the RCD is wired correctly (no faults and high insulation readings), they do not nuisance trip, correct? Tripping always equals earth fault?

Just double checking.
 
An RCD will only trip when there is an inbalance you are trying to find it.

Sometimes there can be circuit protective currents in a system. Not likely in a domestic installation unless there are a lot of switch mode equipment such as TV, Comp games, computers etc.

What have you tested to see what is tripping the RCD. Have you done the basic ie unplug everything
 
Ok, what threw me off was the occasional, random tripping. So this is indeed a current imbalance that needs to be traced.

Is it normal for appliances to trip them?
 
Ok, what threw me off was the occasional, random tripping. So this is indeed a current imbalance that needs to be traced.

Is it normal for appliances to trip them?
Only if the appliance has a fault present
 
As per post #4, have you tested the RCD? Daz
 
Ok, what threw me off was the occasional, random tripping. So this is indeed a current imbalance that needs to be traced.

Is it normal for appliances to trip them?
No, not normal but also not necessarily a fault, could be bad circuit design. The earth (CPC) is functional as well as protective.
 
But if the RCD is wired correctly (no faults and high insulation readings), they do not nuisance trip, correct? Tripping always equals earth fault?

Just double checking.
I take it you mean low insulation reading.
 
could be gremlins. nasty little critters.
 
Do RCDs nuisance trip without an earth fault or is a tripping RCD always the sign of an earth fault?
Are you an Electrician? do you understand how an RCD works? if not and I am being kind- should you be working on circuitry? no offence.
 