I'd agree with everyone above, never disturb the earth clamp on a lead cable unless there's absolutely no other option.. I'm interested to know what your Ze reading was.
I was going to do it earlier - will do it tommorow. Don't I have to do all the tests in order, or can I just go straight to the ZE ?I'd agree with everyone above, never disturb the earth clamp on a lead cable unless there's absolutely no other option.. I'm interested to know what your Ze reading was.
. Seriously though rather stick to the order of testing you've been taught or as it's outlined in GN3.I was going to do it earlier - will do it tommorow. Don't I have to do all the tests in order, or can I just go straight to the ZE ?
Ze 0.29 Ω not a million miles away at allas dave says. diss. your outgoing earths/bondings , and get your Ze. from the block and the incomer L in your CU.
i'll guess at a Ze of < 0.3 Ω
Thanks very much for all the great info and input.
Moving on from the supplier's earth.
The pic below shows Main gas bonding.
Based on the regs I'm convinced I have to upgrade to 10mm
currently there isn't a good connection to the pipe and there's no Label
The main water bonding is on a thiner cable and it's connected to the lead pipe.
Asking for continued assistance........
Does anyone one think I don't need to upgrade the bonding ?
Ha ha I hoped somone would ask me that LOLOk, what size is the bond at the moment?
Can you find a regulation to support your thought that it needs replacing with 10mm?
544.1 table 54.8
My main earth bonding to the Gas and water should be 10mm
514.13.1 no label