Discuss C2 or C3 in the UK Electrical Forum area at ElectriciansForums.net
I would value your opinions on this.
I did an EICR and found two lights in a bedroom that are florescent lights so class 1 but the lighting circuit is old and does not have an earth. However, the lights are in vanity units, so you cannot touch the units without dismantling the vanity units. As they cannot be touched, can the C2 for using an earthed fitting on non earthed lighting circuit be downgraded to C3?
The more I think about it, the more I think it has to be changed to class 2 fittings if the client wants a satisfactory result.
I hope this does not mean you are being told what the outcome is to be ! Is there any other class 1 on the circuit ?.if the rest of the installation is in a good state that would outcome a satisfactory result recommend to the client they are disconnected until earthed
Reply to C2 or C3 in the UK Electrical Forum area at ElectriciansForums.net