T
topcat72
hi all
I am sure this question has been asked many times, however i would like some clarification please.
is there a guide anywhere on here that explains to what extent you should fill in a full electrical installation test cert and what should be entered if you have only installed 1 additional circuit to an existing DB.
It seems a complete waste of time and resource that you should enter limitations for the supply characteristics and earthing arrangements for example, as you cannot be responsible for the condition of the whole installation when only installing 1 new circuit.
it is my understanding that although a minor works should only be used for an alteration for up to 3 additional circuits the information entered into a full electrical cert is only relevant for the new circuit installed.
i hope that makes sense.
thanks in advance
TC
You are not responsible for the whole installation, you are certifying your work.
However the earthing and bonding must be checked and verified as it will effect any work you install. I wouldn't start an install without checking beforehand.
And if it is in your house that you have just secured the mortgage on - remember it is built of extraneous conductive materials. :)
i am fully aware of regulation 132.16 and it states that "the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate"
it is never an option to check the earthing requirements of an existing installation before we carry out an install as it is for tenant sub metering and data logging equipment, obviously as a sparky with 30 years experience it is common sense that such parameters should be checked before carrying out an install, along with polarity and phase rotation, however the cert is only covering the additional circuit not the supply parameters and earthing arrangements.
without carrying out an adiabatic equation it should always be assumed that such parameters were calculated at the design stage of the original install.
i just beleive it is a waste of time as the electrical cert is not bespoke to the additional circuit.
i was after some guidance notes, if anyone can point me in the right direction.
cheers
TC
TC , if you are talking about a new circuit . The EIC requires you to fill in the supply characteristics, earthing type etcetera.
What more were you thinking of adding , or have I completely misunderstood what you are asking. :)
Okay my view is this.......
Adding a new circuit requires an electrical installation certificate.
This certificate should include the earthing arrangement used tn-s etc etc. Any protective bonding conductors serving what services should be confirmed, size recorded,ticked for continuity and verified for suitably of continued service or if inadequate newly installed.
The supply characteristics should be recorded and if the DNO fuse can't be obtained then a not verified/ limitation should be recorded.
Size of supply conductors recorded and material ,earthing conductor bs en of the main switch of the consumer unit.
The schedule of inspections should be ticked off to what is relevant to what you have installed and not any of the other circuits.
The circuit installed then is recorded and tested in the appropriate columns.
Apologies if what I've said is stating the bleeding obvious to yourself but I'm unaware of any guides other than maybe guidance note 3 or the niceic publication guide to inspection and testing amendment 3.
hi Ian
thank you, that is more the confirmation i was after, maybe i havnt explained myself very well, i understand what should be tested and reported, i have and understand gn3 and bs7671, it was just the fact that there is a lot of information required on an EIC that isnt relevant to just adding 1 circuit to an existing installation, it seems a waste of a full cert for 1 circuit.
thank you all for comments.
when we are due our next eca audit i will discuss further with the eca auditor to confirm we are recording the correct info.
thanks
TC
hi Ian
thanks
TC
All the information recorded is to confirm compliance really to bs 7671 and is a source of information for anyone adding/maintaining and testing the installation as long as the documents are to hand and kept safe for future reference.
just to add, in the situation where I'm adding a circuit to an existing CU, I use the word "used" where there is an existing MCB/RCBO in place and "spare" where there is a blank .... then the full details of the circuit I've added.
This then makes it 100% clear what my cert is covering...
Limitations ONLY EVER apply to an Electrical Installation Condition Report. You can't use a limitation relevant to what you are certifying as compliant!
You can verify it - by enquiry.
The DNO isn't always helpful in these matters I've found.
Takes up your own time and costs a small fortune in phone calls getting passed about and put on hold with no answer to your question.
Just not worth the time.
One you ask the customer to obtain he information.
Two you obtain the information and charge the customer for doing such.