J

Jacko

hello,

I'm very new to this trade and do industrial installations. A friend employed an electrician to run a feed to a new consumer unit in his shed so I went to have a look at it out of curiosity to see the correct way it's done. I haven't done any domestic work yet but I don't think it's correct. Could you help please?

It is a PME system. He has taken a 2.5 t+e cable directly out of the 100amp isolator in the suppliers electrical box and run it 5meters in conduit and then under their decking for another 5 meters and the last meter is buried under some cement between patio slabs to supply the new fuse board. The fuse board is rcd protected and has 2 circuits. 1 is a 6amp for one light and the other is a 32 amp for 1 double socket on a radial, not a ring.

It doesn't seem correct to me from listening to more experienced men on site.

Thanks in advance for any help.
 
hello,

I'm very new to this trade and do industrial installations. A friend employed an electrician to run a feed to a new consumer unit in his shed so I went to have a look at it out of curiosity to see the correct way it's done. I haven't done any domestic work yet but I don't think it's correct. Could you help please?

It is a PME system. He has taken a 2.5 t+e cable directly out of the 100amp isolator in the suppliers electrical box and run it 5meters in conduit and then under their decking for another 5 meters and the last meter is buried under some cement between patio slabs to supply the new fuse board. The fuse board is rcd protected and has 2 circuits. 1 is a 6amp for one light and the other is a 32 amp for 1 double socket on a radial, not a ring.

It doesn't seem correct to me from listening to more experienced men on site.

Thanks in advance for any help.
Where did "The Electrician" that did this park his Horse
 
No mate, it's not a wind up.

I don't know if there is conduit between the slabs because he has cemented over it but the chase looks to thin.

The socket only has 1 x 2.5 cable going to it and it's on a 32a mcb

The supply cable (2.5 twin and earth) is going from the 100amp cut out switch in the electric cupboard straight into the new db in the shed
 
No, he hasn't got a certificate.

If you have the time could you please tell me how it's installed incorrect and what he should have done?

I'm assuming he should have taken the supply from the main db in the house? Not the main electric cupboard?
 
It should have been taken from a suitable source (ideally spare MCB/RCBO in the CU, but possibly spurred from RFC depending on load).

The cable should have been selected and routed appropriately to the conditions (sounds like SWA would have been more suitable).

The 32A MCB for the 2.5mm radial is incorrect.

On the good side, the 6A lighting circuit sounds OK!

I'm assuming you know from your industrial sparky work that a 2.5mm cable is not suitable for feeding from a 100A supplier fuse?
 
Yeah, I thought the 2.5 cable was wrong but wasn't 100% sure because the circuits in the shed are protected by their own mcb.

I don't understand the domestic side of it between the 100a fuse and the new db.

I know the socket should be on a 16/20 amp mcb
 
2.5 T/E from the suppliers side cutout ? So he's broken into & tampered with suppliers equipment ? If that's the case then it's illegal to start with.

2.5mm T/E off a 100 amp switch so no protection: Lethal

Cable feeding outside without RCD protection, so contravenes BS7671.

Don't think we need to go further.
 
Lanky, when I said I'm new to the trade, I'm an apprentice only a few months in so have next to no experience.

Specialist, the 2.5 supply is taken from the loads side of the 100amp isolator.
 
Yeah, I thought the 2.5 cable was wrong but wasn't 100% sure because the circuits in the shed are protected by their own mcb.

I don't understand the domestic side of it between the 100a fuse and the new db.

I know the socket should be on a 16/20 amp mcb

This may come across as rude, but do you see anything worrying in an industrial electrician saying this?
 
When I said I'm an industrial electrician, I should have said I'm 3 months in to an apprentiship and working on my first ever industrial installation.... basket and tray at the moment. That is as far an my electrician knowledge goes at the moment. I should have been more clear sorry
 
He said he is new to this trade and works on industrial,I would expect he is training
Am I right Jacko?

What area of this lovely land of ours did this recent escapade take place
 
When I said I'm an industrial electrician, I should have said I'm 3 months in to an apprentiship and working on my first ever industrial installation.... basket and tray at the moment. That is as far an my electrician knowledge goes at the moment. I should have been more clear sorry

Ah, that changes things slightly :-)
Seriously though, advise your friend to get the circuit re-wired correctly as it is dangerous if left as-is.
 