You should have the cpc connected to the earth bar.Left all mains on to rest of house as they wouldn't have juice off while in there !
Just pulled related L,N,E from terminals at Cu to test
You should have the cpc connected to the earth bar.Left all mains on to rest of house as they wouldn't have juice off while in there !
Just pulled related L,N,E from terminals at Cu to test
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPCI still don't understand why you have left them open.
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPCI still don't understand why you have left them open.
Always done IR with every conductor out and in croc clips ? NIC assessor said was right way ? Thought would cause parallels if left in Earth bar ! Maybe I've made a fundamental boo booYou should have the cpc connected to the earth bar.
Never isolate the cpc from the main mass of earth.I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC
Always done IR with every conductor out and in croc clips ? NIC assessor said was right way ? Thought would cause parallels if left in Earth bar ! Maybe I've made a fundamental boo boo
was the customer biting on your ear!Thanks Lee, I'll try next time when customers not being a pita !
True, thanks, just builder wanted lights in and on during the ongoing works tiling etc.. so been on / off throughout job !RE awkward fittings and dimmers ..... Just fit standard switches and omit light fittings and do continuity and ir tests first ...... Can save hours of hassle
Bit of a hitler the wife there !was the customer biting on your ear!
True, thanks, just builder wanted lights in and on during the ongoing works tiling etc.. so been on / off throughout job !
The 17th Edition requires the cpc to be connected to the Earthing arrangement before conducting insulation resistance tests - therefore the cpc should NOT be removed from the Earth bar. Otherwise a fault to Earth that isn't a fault to the cpc won't be detected.Just pulled related L,N,E from terminals at Cu to test
ThanksThe 17th Edition requires the cpc to be connected to the Earthing arrangement before conducting insulation resistance tests - therefore the cpc should NOT be removed from the Earth bar. Otherwise a fault to Earth that isn't a fault to the cpc won't be detected.
Will do & with main switch open too !I suggest you retest with the cpc connected to the earth bar, close all switches and retest, use 250v if you are concerned.