I still don't understand why you have left them open.
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC
 
I still don't understand why you have left them open.
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC
You should have the cpc connected to the earth bar.
Always done IR with every conductor out and in croc clips ? NIC assessor said was right way ? Thought would cause parallels if left in Earth bar ! Maybe I've made a fundamental boo boo
 
Won't fry anything and I only ever resort to 250v if I get odd readings to cancel out possible filtered equipment.
 
RE awkward fittings and dimmers ..... Just fit standard switches and omit light fittings and do continuity and ir tests first ...... Can save hours of hassle
 
I figured in my early testing career that it would save frying any LED downlights or dimmer module etc.. as would take a good while to disconnect all fittings / lamps etc.. straight away. Tested at 100 & 250 V too to save any issues but none would ramp up test voltage to CPC

Always done IR with every conductor out and in croc clips ? NIC assessor said was right way ? Thought would cause parallels if left in Earth bar ! Maybe I've made a fundamental boo boo
Never isolate the cpc from the main mass of earth.
 
RE awkward fittings and dimmers ..... Just fit standard switches and omit light fittings and do continuity and ir tests first ...... Can save hours of hassle
True, thanks, just builder wanted lights in and on during the ongoing works tiling etc.. so been on / off throughout job !
 
I suggest you retest with the cpc connected to the earth bar, close all switches and retest, use 250v if you are concerned.
 
The 17th Edition requires the cpc to be connected to the Earthing arrangement before conducting insulation resistance tests - therefore the cpc should NOT be removed from the Earth bar. Otherwise a fault to Earth that isn't a fault to the cpc won't be detected.
Thanks
 
If the neutral is disconnected you don't need the main switch off but with your tester backing off with the L/N to earth test maybe you have a fault. I don't use an mft to understand their quirks, life is too short:D
 