Hi chaps,
So last weekend I inspected a small office building, overall it's in good condition and there is nothing to make me think the installation is not safe for continued use except some exposed basic insulation in the wiring closet, an RFC with a CPC continuity of 0 ohms (think it's joined in a junction box behind the CU where the cables were extended (same reason the basic insulation is exposed - bad extensions on CU change) and some enclosures that don't provide the required level of IP protection (dry lining boxes which are not enclosed at the rear). I also noted a couple of issues regarding the bonding to the gas.
Issue 1 - The clamp is way over 600mm from the building entry point and there is no reason for this (except maybe the situation described in issue 2) as the entry point is in the same wiring closet as the current clamp. So that's a C3, it could be improved.
Issue 2 - The pipework comes in, splits into two branches. The clamp is shortly after the branch. The other side of the branch goes through a valve, both segments disappear into the fabric of the building. Obviously I can't establish whether if any of the branches or valve are disconnected the disconnected segment would be considered as extraneous, but given it disappears into the building and could be touching god knows what, I was planning on adding a C3 observation recommending the gas bonding be extended to connect the two segments after the point at which they could be disconnected.
Issue 2 is the one I'm struggling with in my mind, because I'm acutely aware that adding bonding could create a dangerous situation, but I'm also aware that if a gas man rocks up and disconnects a branch the chances of him sorting the bonding are practically nil.
I've checked GN8, the regs and spent quite some time looking for an answer but I can't find anything about how to handle this kind of split in the pipework.
Comments and thoughts please
So last weekend I inspected a small office building, overall it's in good condition and there is nothing to make me think the installation is not safe for continued use except some exposed basic insulation in the wiring closet, an RFC with a CPC continuity of 0 ohms (think it's joined in a junction box behind the CU where the cables were extended (same reason the basic insulation is exposed - bad extensions on CU change) and some enclosures that don't provide the required level of IP protection (dry lining boxes which are not enclosed at the rear). I also noted a couple of issues regarding the bonding to the gas.
Issue 1 - The clamp is way over 600mm from the building entry point and there is no reason for this (except maybe the situation described in issue 2) as the entry point is in the same wiring closet as the current clamp. So that's a C3, it could be improved.
Issue 2 - The pipework comes in, splits into two branches. The clamp is shortly after the branch. The other side of the branch goes through a valve, both segments disappear into the fabric of the building. Obviously I can't establish whether if any of the branches or valve are disconnected the disconnected segment would be considered as extraneous, but given it disappears into the building and could be touching god knows what, I was planning on adding a C3 observation recommending the gas bonding be extended to connect the two segments after the point at which they could be disconnected.
Issue 2 is the one I'm struggling with in my mind, because I'm acutely aware that adding bonding could create a dangerous situation, but I'm also aware that if a gas man rocks up and disconnects a branch the chances of him sorting the bonding are practically nil.
I've checked GN8, the regs and spent quite some time looking for an answer but I can't find anything about how to handle this kind of split in the pipework.
Comments and thoughts please