Hi chaps,

So last weekend I inspected a small office building, overall it's in good condition and there is nothing to make me think the installation is not safe for continued use except some exposed basic insulation in the wiring closet, an RFC with a CPC continuity of 0 ohms (think it's joined in a junction box behind the CU where the cables were extended (same reason the basic insulation is exposed - bad extensions on CU change) and some enclosures that don't provide the required level of IP protection (dry lining boxes which are not enclosed at the rear). I also noted a couple of issues regarding the bonding to the gas.

Issue 1 - The clamp is way over 600mm from the building entry point and there is no reason for this (except maybe the situation described in issue 2) as the entry point is in the same wiring closet as the current clamp. So that's a C3, it could be improved.

Issue 2 - The pipework comes in, splits into two branches. The clamp is shortly after the branch. The other side of the branch goes through a valve, both segments disappear into the fabric of the building. Obviously I can't establish whether if any of the branches or valve are disconnected the disconnected segment would be considered as extraneous, but given it disappears into the building and could be touching god knows what, I was planning on adding a C3 observation recommending the gas bonding be extended to connect the two segments after the point at which they could be disconnected.

Issue 2 is the one I'm struggling with in my mind, because I'm acutely aware that adding bonding could create a dangerous situation, but I'm also aware that if a gas man rocks up and disconnects a branch the chances of him sorting the bonding are practically nil.

I've checked GN8, the regs and spent quite some time looking for an answer but I can't find anything about how to handle this kind of split in the pipework.

Comments and thoughts please :)
 
If I've understood correctly ... the gas pipe enters, could be bonded, but is not. The pipe then has a branch and one branch is then bonded. Possibly C3 as an improvement for it to be put closer to the point of entry and before branching.
I like to take a walk with wander and confirm continuity of the cables and their connection to the pipework. Testing where the branching gas pipe reappears will reveal if its still bonded correctly, or if dis is it "extraneous and wants bonding, or its just a piece of metal" as Chris Kitcher has said in one of @Pete999 videos.
 
Bs 7671 recommends 600mm from point of entry if external and before any branches where practical.
That said if it's bonded then there is no safety issue in my opinion if you have access to the actual clamp and connection.
I would add a note in the comments section but if adequately bonded through out its length then there's no safety issue for me.
It maybe a non compliance but I don't think it gives rise to danger if indeed it's bonded through out.
 
Last edited by a moderator:
I don't do EICR's, so can't help with that coding malarkey.

This is some guidance I received from Elecsa Tech re bonding of services with mixture of plastic & metal. Perhaps it could assist your decision making with the branched pipe?

'In an installation where there is a mixture of plastic and before applying protective bonding to the metal pipework it has to be established that any metal pipework is introducing a potential and is accessible with another conductive or extraneous conductive part.
Testing may be carried out where practical to establish whether the metallic pipework is introducing a potential. Guidance on acceptable values of resistance can be found in section 6.1 of Guidance Notes 8.

It is important when choosing to carry out this test that any parallel earth paths are removed to obtain an accurate value. We would therefore recommend that the installation is first safely isolated. The main earth is then removed and a resistance test be carried out between the main earth and the pipework concerned. When the value had been obtained the main earth must be re-instated before energising the installation again.
Where the tester choses to use one of the reference values in GN8 and the measured value exceeds the calculated vale main protective bonding would not be required'.
 
You are not in a position other than physically looking ,to test that branch in isolation to tell whether it is extraneous or not,it is one system and requires one bond

It may exit and enter again to become extraneous in its own right but you are not to know other than looking at the run that is visible

I wouldn't concern myself with the make up of the gas circuit unless it was obvious there is more than one entry point
The clamp position is not correct and should be recommended to improve
 
I'm happy it's bonded (I carried out some long lead tests and got suitably low continuity reading back to the MET), but the clamp is in the wrong place hence the C3 for that, it's just the presence of the valve and the fact there are two branches, which could potentially be disconnected at some point in the future.

Tracing the pipe fully isn't possible as it disappears into the building fabric, but it reappears at the boiler where there is supplementary bonding anyway, and in another location near the main water bonding where about 5 pipes are all bonded together.

So no code or comment for the branch :)

Thanks guys.
 
I can't see how you can code it a C3.
They are instances were it's impractical to bond were the pipework enters a property from the outside when the pipework is inbedded in the wall behind plaster or dry wall, so the most practical point could be the boiler.
So by doing this it's not bonded within 600mm of point of entry but it doesn't make it unacceptable, it's the practicability of it.
The regulations do say where practical the connection shall be made within 600mm , key word being practical.
Your installation it maybe practical to have bonded it there but I can't see how it's a safety issue if there's a bonding connection in place to start with.
More worthy of a comment I'd say.

I await everyone else's disapproval of my comments :)
 
I see where you're coming from Ian. The practicality of bonding it in the correct location... I have no clue as to why they didn't do it properly in the first place because the pipe enters the building in the wiring closet where the MET is, the same closet it is currently bonded in.

In terms of affecting the safety, I agree, it doesn't affect safety as there is very definitely a good connection. I think it's just down to my interpretation of what warrants a C3 classification and I am perhaps being a little too broad with it instead of only applying it to items relating to safety.
 
I can't see how you can code it a C3.
They are instances were it's impractical to bond were the pipework enters a property from the outside when the pipework is inbedded in the wall behind plaster or dry wall, so the most practical point could be the boiler.
So by doing this it's not bonded within 600mm of point of entry but it doesn't make it unacceptable, it's the practicability of it.
The regulations do say where practical the connection shall be made within 600mm , key word being practical.
Your installation it maybe practical to have bonded it there but I can't see how it's a safety issue if there's a bonding connection in place to start with.
More worthy of a comment I'd say.

I await everyone else's disapproval of my comments :)
I agree with most of what you have written, however to be accurate it is "where practicable", NOT "where practical". I only point this out as the words have differing meanings.
 
I agree with most of what you have written, however to be accurate it is "where practicable", NOT "where practical". I only point this out as the words have differing meanings.
Indeed you are correct
A miss use of words but hopefully people get what I meant.
 
Not a C3 in my opinion, moving the bond won't offer a safety improvement, it will only improve your bank balance.
 
I'm not going to classify the bonding clamp location, and the fact the pipe splits, if it changes I'm sure that will be dealt with properly ;)

As for improving my bank balance, wasn't planning on quoting for the C3s (apart from labelling everything as it should be which won't take too long), only the few C2s (mainly access to live parts and insulation outside of enclosures in accessible places).
 
If the gas pipe is bonded the installation is safe for continued use.. your making a mountain of a mole hill. Dont worry about covering your ---,, have some confidence in your decisions SC.!
 
If the gas pipe is bonded the installation is safe for continued use.. your making a mountain of a mole hill. Dont worry about covering your ---,, have some confidence in your decisions SC.!

Will do :)

I'm going to be breaking the 600mm rule myself if one of my quotes gets accepted. CU move, gas bond has already been disconnected when the old pipe was decommissioned... gas man left it neatly tucked away behind the meter board so no one would notice. Getting a bond to the front of the house isn't practical without mass upheaval which the customer doesn't want so I'm going to bond to the pipe in the floor void above the CU.

That I have no problem with, but commenting on existing installations... I worry :)
 