Hi all,
Hoping for some advice, I ran a cable to some light fittings some time ago during refurb of my place. I've now gone (2 yrs later) to connect that light fitting... and nothing. Dead.
I wired my place all myself, then had a spark come and sign it off. All connected circuits passed with flying colours. FYI, as that circuit was not connected it was not tested.
I've rewired, reframed, plastered and fitted cornice. All of which might have brought the chance of a screw or some other damage hitting the cable after it was run.
The live feeds through the house run to all the light switches, in this case a 4-gang dimmer. Two of the gangs are connected and running. So the live feed is fine.
Then from the switch this particular run of 1.5 T&E heads up a wall, across a section of ceiling then behind the cornice to a wall light. I ran a 9v battery on the pos only then back to the battery via my multimeter with a long cable to check continuity. I then did the earth and the neg separately the same way. The earth and the neg test ok. The live is dead.
This cable must have a break somewhere, or taken a screw hit.
When I connected the switch and the light, the breaker/RCD doesn't trip
so if it is a screw it's broken the live and not disturbed the Earth or Neg. Which is a bit weird.
So hoping to get some tips. Especially to avoid making a load of holes in my lovely cornice.
Thanks in advance.
Greg
Hi CP and Welcome to the Forum!
Cable breaks can be tough to find and it does take some experience. If you do find the break it's likely under something and how will it be fixed? Agree @kingeri - replace the cable :)
No I've not used one. Was looking at something like a Fluke 2042 Cable Fault Locator
I understood jointing cables inside walls/floors was allowable as long as you used a maintenance-free junction/terminal.
So not convinced the entire cable needs to be replaced.
So just to confirm. As you say, the live at the switch is ok. You think you have a break in the live cable between the light switch and the light.
Get yourself a tester that can test the cable is live without damaging the insulation and test the live cable in different sections. Test it where it goes into the ceiling, then you will know if that part of the cable is fine... and so on..
OP, with all respect, you admit you energised this in the knowledge it hadn't been tested. This in itself was unwise. By the time you have hired a tester, figured out how to use it, realised you likely will still need to punch holes in ceiling and wall anyway, it would be easier and probably quicker to replace the cable. Or get an electrician to do it (shock horror).
How are you defining 'Dead'?
Choices are:
Line (aka Live) Open circuit (OC)
Neutral OC
Both Line and Neutral OC?
Is the CPC (aka Earth) also OC or do you have continuity from the general area of the switch to the end of the cable?
As far as screws through cables - I've generally found they cause a short circuit rather than a break in the cable. More likely to have trapped a cable behind plasterboard or something of that ilk.
Is there any junctions present in the cable run? A loose connection would be a more likely candidate IMHO.
I use a great bit of kit for finding breaks and shorts in cables but it was expensive (£150+), but as good as it is, it still requires chipping away plaster to effect a repair.
To be honest my friend, it may well be quicker and cheaper to get an electrician in for a couple of hours...
Here's a thought - it's definitely the right cable isn't it? After two years I'm not sure I'd remember exactly what I'd done - these days have issues remembering what I did yesterday!!
Identify the cable (beyond all doubt) by end-to-end testing with both ends open-circuit...
Is/has the cable in question been/or is connected to anything? or is it just a piece of cable buried in the building fabric?
You'd need to test the Insulation Resistance (IR) of the cable. That will show whether there is damage to the Line, Neutral and/or cpc conductors.. My thinking here is that if the Line is oc due to crushing or screw damage, then it's likely that the others are damaged too.
You'd be looking at an IR of 100's of M-ohms. In order to conduct the test you'd need to have an appropriate (and calibrated) test instrument. Mine cost me £650 five years ago....not sure whether you can hire one.
You'd be looking at an IR of 100's of ohms. In order to conduct the test you'd need to have an appropriate (and calibrated) test instrument. Mine cost me £650 five years ago....not sure whether you can hire one.
In my opinion, for a Diyer to hire a MFT or IR tester will be a waste of time, he needs to hire a Spark for a few hours to rectify the fault.
As @Wilko said in post #8, it is a guaranteed fix.
You can also crimp or solder cables together, as long as you do a proper job. I would, whenever possible, replace the cable.
I once had a break in a brand new "un damaged" cable, a leg of the RFC. It turned out to be a faulty piece. Fortunately I had installed it neatly in capping so although now newly plastered I was able to pull a new leg in.
The moral of the story being that care and attention during installation pays dividends even when least expecting.
My gas boiler was broken down in my house 2 weeks ago and i certainly didnt try to fix it. I hired a qualified competent person to do it properly and safely. Electric is just as dangerous..
I think not..
Gas is way more dangerous. Electricity will usually kill one person. Gas on the other hand can take down houses... killing a lot more than one..
Is it any better than one person would be to die because of electricity rather than a group in a gas explosion? Or would it be better if the work was carried out and tested by a competent person and no one died
How about 'The work is carried out correctly and no one dies'.
The OP is trying to find and fix a bust wire..
Well that's my view on DIYers trying to save a few quid and the possible consequences. I guess we will agree to disagree.
Everyone tries to save money mate.. If they can.
We don't know the OP. He might be interested in sorting this out himself. Improve his knowledge of things. Who knows... He's most prob buggered off now..... can't blame him...
My response to all DIYers. My gas boiler was broken down in my house 2 weeks ago and i certainly didnt try to fix it. I hired a qualified competent person to do it properly and safely. Electric is just as dangerous, so why do so many DIYers mess with it?
My boiler broke down 5 years ago, researched the issues took the logic board out re-soldered the dry joints and put it back together still working.
Don't be afraid of gas, washing up liquid or a match are the two best tools to have. ;o))))
I don't think anyone disagrees with you, electricity can be extremely dangerous. I think in this situation its more about the context.
A work colleague of my partner passed away a few years back due to a poorly fitted flu on a gas fired boiler. She was slowly poisoned by carbon-monoxide over a few weeks.
Just as easily a poor electrical connection may result in arcing then fire and could cause just as a serious fatality.
Both gas & electricity should be respected since both can cause serious damage, injury or death if mis-used/neglected.
My boiler broke down 5 years ago, researched the issues took the logic board out re-soldered the dry joints and put it back together still working.!
Replacing/repairing a PCB is a little different than working on the gas/burner &/or emissions part of a boiler. I'd still would have had it tested to make sure it was burning efficiently and cleanly & that the emissions were still being properly vented!
There was no mention of the work carried out just that the biller bike down, in my rental every often I had to go and pump the pressure vessel up to the correct pressure.
London
How to trace a break in a cable? In a wall!
competant person,
Lou,