Hi Guys!

I've worked with a few qualified-electricians recently and I'm shocked with the large-scale misconceptions regarding the proper safe-isolation procedure, particularly concerning the function of an AVI (Approved Voltage Indicator).

During the last few weeks I've met several domestic qualified-electricians who have told me not to test between line-earth & neutral-earth because this will trip the RCD/RCBO; they have all advised me to only test between line-neutral. When I confronted them with actual facts and figures, they all refused to acknowledge my comments, arguing otherwise without any form of proof, which I found bizarre?

I'd like to confirm that their advice is incorrect, and I can prove it factually. I use a Kewtech KT1790 Approved Voltage Indicator which seems fairly common amongst electricians, and I'll base my comments on this:

  • The Kewtech KT1790 data-sheet states "This instrument can make measurements between L-PE without tripping RCDs".
  • The Kewtech KT1790 data-sheet states that the devices internal-resistance is 200,000 Ohms. Based on this value, we can calculate the current-flow using basic Ohm's Law:
    - 230V - 1.15 mA (Standard RMS voltage used for design calculation)
    - 245V - 1.22 mA (Highest likely RMS voltage measured)
    - 500V - 2.50 mA (Exceeding AC Peak Voltage)
  • A common RCD used in domestic properties for additional-protection has an operating-current of 30mA (much greater than the current produced while testing).
  • Rarely in specialised circumstances a 10mA RCD is used for certain applications (much greater than the current produced while testing).
To conclude, the AVI (Approved Voltage Indicator) is perfectly suitable and safe for use when performing the proper safe-isolation procedure (including testing between line-earth and neutral-earth) as explicitly explained within the products data-sheet, and also proven through simple calculation of it's specifications.

I'm interested to find out if anyone else has encountered this problem? If so, to share this information.
 
They've had experience of older basic testers (pre LED) which did trip RCD / RCBO and not bothered to try with the newer non trip ones.
 
I've worked with a few qualified-electricians recently and I'm shocked
You say you are shocked, so much for safe isolation. If someone you work with wishes to chance getting an electric shock just make sure you know appropriate resuscitation techniques. Apart from warning someone what can you do. As for Popular Misconceptions, it certainly has not been my experience that this is endemic in the trade most people I have met take all due precautions. I also add to persons who sometimes work/train with me that they should test between local metal work and earth to ensure there are no stray voltages such as suspended ceilings when working on klik fittings above. I have found 120v on suspended ceilings before. So think about that as well.
 
The Fluke T-150 has an RCD trip function built in, so you can test at a circuit and trip the RCD by pressing two buttons (one on the dumb probe and one on the main unit).

But regardless, they are wrong. Safe isolation requires a full test of L-N, L-E and N-E.
 
shoot them down with this then.

example is a lost N, so test L-N, no reading. then get a belt off the L. maybe their thinking is because L-E and N-E tests are covered in week 6 of their 5 week course.
 
shoot them down with this then.

example is a lost N, so test L-N, no reading. then get a belt off the L. maybe their thinking is because L-E and N-E tests are covered in week 6 of their 5 week course.
 
First they are very very wrong
Second,my advice for anyone interested, learning or even qualified in electrics, it is to never under any circumstances accept assurance off anybody but yourself that something is safe or even advice on how to make something safe

Its your health and well being at stake and its too important to trust to anybody irrelevant of whether they appear to know what they are doing
 