Just replacing like for like luminaires.

If you can imagine, the rest of the refurb is fancy tiling, shower screens, furniture etc. Do I have to put that ec clamp on the bottom of their nice new chrome towel radiator?

Edit, oh and moving extract fan into loft space.
Therefore if you are altering a circuit in a bathroom then RCD protection is required.
 
if you cant put a rcd in c/u put one outside the bathroom .
You could put one in front of the CU, would be easier than faffing with the bathroom circuits, I would think. Still think he is wrong to use the 30 Amps in his calculations. In the video CK is using 10ma as quoted in GN3 not a current that operates an RCD 230/.01 (10ma)= 2300ohms minus the resistance of the body ohms1000, in that calculation there is not any reference to the operating current of any OCPD, only referring to GN3.
 
upload_2018-1-8_19-7-32.png
one of them alterations to the bathroom circuit .
 
I have clarified this particular point before wid' my scheme. If there are no alterations to the circuits, replacements are like for like, then there is no requirement to install additional protection.

Imagine if you replace a pull cord, sorry Madame I now have to install you an RCD FCU.

Now what about that towel radiator?
 
You could put one in front of the CU, would be easier than faffing with the bathroom circuits, I would think. Still think he is wrong to use the 30 Amps in his calculations. In the video CK is using 10ma as quoted in GN3 not a current that operates an RCD 230/.01 (10ma)= 2300ohms minus the resistance of the body ohms1000, in that calculation there is not any reference to the operating current of any OCPD, only referring to GN3.
The formula given to determine the effectiveness of supplementary bonding in bs 7671 is 50v /Ia ( or I delta N when the circuit is protected by an rcd) to effectively make sure the touch voltage will not rise above 50 volts during a fault as long as the resistance of the pipework is below in this case 1.666 ohms.
So how is it wrong?
That video is for determining pipework is an extraneous conductive part like your water and gas services to see if they require protective bonding.
 
Last edited by a moderator:
I would use the highest rated device on the installation as a fault occurring anywhere in the property could impact the bathroom.
 
I would use the highest rated device on the installation as a fault occurring anywhere in the property could impact the bathroom.
That is not what bs 7671 says on the matter.
It’s the protective device for that particular location
 
The formula given to determine the effectiveness of supplementary bonding in bs 7671 is 50v /Ia ( or I delta N when the circuit is protected by an rcd) to effectively make sure the touch voltage will not rise above 50 volts during a fault as long as the resistance of the pipework is below in this case 1.666 ohms.
So how is it wrong?
That video is for determining pipework is an extraneous conductive part like your water and gas services to see if they require protective bonding.
No the video is explaining how to test pipework to see if they require any supplementary bonding, there are other tests to ascertain that main bonding is up to scratch.
 