I was thinking more of 314.1:

Every installation shall be divided into circuits, as necessary, to:

(i) avoid danger and inconvienience in the event of a fault.


And

314.2:

Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such a way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device.
I already quoted 314.2 ("due account shall be taken..."). 314.1 requires the installation to be divided into circuits - this has nothing to do with the RCCB. The overcurrent protective device connected to that circuit is what makes it a separate circuit. (See the definition of "circuit" in Part 2.)
 
There is always exceptions but only lazy electricians put in RCD protection where it is not required in my opinion.
Rubbish. Providing RCD protection to BS1363 socket outlets was forward thinking rather than lazy. Particularly in non-domestic installations there certainly are circumstances where it is advisable to avoid RCD protection where allowable but this certainly isn't an example of that. If non-RCD protected socket outlets were to be incorporated in a non-domestic installation then really I would expect to see a non-standard socket outlet rather than BS1363 outlets. (Incidentally, this is a requirement of the Wiring Rules in the south of Ireland where RCD protection of all socket outlets has been mandatory for decades.)
 
I personally would not even code a single rcd protecting an installation in a domestic setting if I saw it during an eicr.
I know that’s not the issue here but let’s not lose perspective that it’s not the end of the world.
 
We all know what the definition says.
According To the definition, my fridge freezer is a circuit.
You however seem to have misread the definition.
The part where it states: “protected against overcurrent by the same protective device(s)”.
 
I personally would not even code a single rcd protecting an installation in a domestic setting if I saw it during an eicr.
I know that’s not the issue here but let’s not lose perspective that it’s not the end of the world.

It is a C3 all day long.

If it was acceptable then we would not be bothering with split load CUs or RCBOs. We would just wack an up-front RCD on everything. We don’t do this because it is not to Regs and shoddy.
 
It is a C3 all day long.

If it was acceptable then we would not be bothering with split load CUs or RCBOs. We would just wack an up-front RCD on everything. We don’t do this because it is not to Regs and shoddy.
no it’s poor practice which is why we provide 2 or more in an installation
A C3 implies a safety issue which I personally don’t agree however like most people I view a single main switch rcd as poor practice
 
I personally would not even code a single rcd protecting an installation in a domestic setting if I saw it during an eicr.
I know that’s not the issue here but let’s not lose perspective that it’s not the end of the world.
Likewise, unless I had evidence that it was causing excessive nuisance tripping.
 
We all know what the definition says.
According To the definition, my fridge freezer is a circuit.
You however seem to have misread the definition.
The part where it states: “protected against overcurrent by the same protective device(s)”.
I haven't misread the definition. My point is that an RCCB does not provide overcurrent protection, therefore isn't relevant to a Regulation requiring division of the installation into circuits.
 
Safer than what? Is an RCD protecting cables buried in a wall safer than metallic conduit protecting cables in a wall?
No-one suggested that earthed metallic conduit wasn't better. The reality is that in a domestic installation it's not going to be a cost-effective solution though.

That said, I previously did additions in my property in 6491B in earthed metallic conduit. However, when I replaced the DB a couple of years ago I had to provide RCD protection to everything due to other parts of circuits having buried T&E etc.
 
So it's not safer then? You actually think it is not safer? Explain please.

Not necessarly no. It would be your design that would determine if it was safer or not. You seem to have an RCD everything approach without any real though or design behind your reasoning.
 
Is having a single RCD that never gets tested safer than not having any RCD at all?
Is having a single RCD that never gets tested safer than having separate RCBOs that never get tested?
If RCDs are so much safer, why are they no an option for cables above ceilings and below floors?
 