I already quoted 314.2 ("due account shall be taken..."). 314.1 requires the installation to be divided into circuits - this has nothing to do with the RCCB. The overcurrent protective device connected to that circuit is what makes it a separate circuit. (See the definition of "circuit" in Part 2.)I was thinking more of 314.1:
Every installation shall be divided into circuits, as necessary, to:
(i) avoid danger and inconvienience in the event of a fault.
And
314.2:
Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such a way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device.