Nigel
.............
No-one suggested that earthed metallic conduit wasn't better. The reality is that in a domestic installation it's not going to be a cost-effective solution though.
There are plenty of other reasons to provide additional protection by means of a 30mA RCD than cables concealed in the walls, however.Nonitnwas soecificall stated that outting in RCDs made installations safer. My point is that nobody can make a blanket statement like that. It shows no thought and is lazy.
There are plenty of other reasons to provide additional protection by means of a 30mA RCD than cables concealed in the walls, however.
I often take that approach. However where it comes to a domestic premises (which must be taken not to be under the control of a skilled or instructed person (and yes, I know these terms have been changed)) then it isn't necessarily a sensible or the best approach.if an installation can be designed and installed without the need for RCDs and meet BS7671 then I will do so.
You need to consider the situation as presented in the OP and not the strange world you seem to reference. In the real world, anyone who doesn't think that providing RCD protection for socket circuits in rented accommodation is more than "lazy". I would like to see you weedle your way out of it if you were ever in front of a judge, should a tenant end up dead in such circumstances, for the sake of fitting an RCD. just get real!No it was specifically stated that putting in RCDs made installations safer. My point is that nobody can make a blanket statement like that. It shows no thought and is lazy.
Well you might not have noticed but we are talking about just such a setting, so it seems to me you are talking out of your proverbial.I understand that. I am the one arguing for thought behind the use of RCds. Not the RCD everything because it is safer.
I accept that in some cases it is safer. But this is not always the case and the use of RCDs should be thiught out and only used if required.
Personally an RCD is a last resort for me. I except I do not work in a domestic setting but if an installation can be designed and installed without the need for RCDs and meet BS7671 then I will do so.
OMG, the WHOLE installation is off, the world has ended. But no one has died.Ok, so an RCD has been fitted instead of the existing DP isolation switch. So, it has now been deemed safer. But...it still doesn't comply.
When RCD operates, the whole installation is switched off. Now, by todays standards is that correct? Solved one problem created another.
Well you might not have noticed but we are talking about just such a setting, so it seems to me you are talking out of your proverbial.
Depending of course on circumstances.OMG, the WHOLE installation is off, the world has ended. But no one has died.
The whole idea of a part RCD spilt board, was so that the lights remained on for safety reasons when RCD operated. Then later it was deemed that dual RCD boards would be fitted as standard in domestic properties to increase safety.OMG, the WHOLE installation is off, the world has ended. But no one has died.
Whats that got to do with it, exactly?Providing RCD protection is not really at issue here.
The issue is using a single device to protect multiple circuits, instead of individual devices for each circuit.