Guest viewing limit reached
DPG
Patron
What's your thoughts on this install done by a utility company? No prizes, just for fun :-)
It was found with the fuse carrier in place. This was removed on safety grounds, bearing in mind the interesting configuration of the supply. It was a colleague of mine who discovered it - and apparently 2 other properties in the block were wired in exactly the same way. So a phone call was made to advise them to point out the installers possible lack of knowledge of cut-outs.
Hahahahaha that's priceless. SP-N, a.k.a 1-phase 1-wire. Some numpty has put blue ties on two of those tails though.
Presumably the installer had had some training to be let loose in society. One has to wonder what was not happening in his mind to recognise the mistake for himself. Even highly trained folk make cognitive mistakes - air line pilots for example, especially if they repeat the same thing over and over again. It is not unknown for airliners to attempt to land with the under carriage still up.
See: El Al pilots forget to lower wheels on Heathrow landing - https://www.timesofisrael.com/el-al-pilots-nearly-try-landing-with-wheels-up/
Well yes, even if the meter is internally isolated you've got the Line available. Make safe the end of the brown tail in the DB, put blue in Line and green/yellow in Neutral, knock a rod in for the earth, pop the bullet in and seal it up so it all looks pukka and away you go.
Looks like there is a link
Looks like the brass block on the right is a 3 way terminal block. 2 neutral conductors and 1 earth conductor.
Nope can't see it neither :( if this arrangement is pme with a split con supply cable, neutrals and earths twisted, taped by black tape, connected to the brass block on the right at the bottom where is the connection/link between the top neutral from the meter and earth?? o_O
if not pme and depending on split/straight con cable type then neutrals and earths would need separate termination...
Rustynails, I think you're missing the point as regards how the neutral has been connected in this example.
Surely a functional test would have picked this up as nothing could work - Line and Neutral will be at the same potential. Unless I've completely misunderstood.
Erm....
How should it look?
There you go I said it.
What I mean is that my first reaction to this image was that you can see the brown line into the carrier without any mechanical protection. Surely this is not how you split supply line and neutral at the cutout?
Yet I take it that the fuse carrier should just have line in/line out, and that the neutral should come out the top of the right hand terminal block.
I need educating.
DPG
Patron
S Yorkshire
Other
If other, please explain
C&G 17th edition regs
C&G 2382-18 (18th edition regs)
C&G 2394 Inspection & Test
C&G PAT
2 x BPEC electrical courses/exams
Interesting cut-out and meter install
DPG,
Selfmade,