[QUOTE="Michaelwgroves, post: 1454180, member: 68265"
But I assume there is a reg that says switch must be in close proximity to shower?
Don't assume, find out. There is no such reg.
[QUOTE="Michaelwgroves, post: 1454180, member: 68265"
But I assume there is a reg that says switch must be in close proximity to shower?
MIs are guidance only, and don't have to be followed, especially when they are wrong.
It’s not so much that they are wrong (though sometimes they clearly are), as whether non-compliance with an MI is a non-compliance with the Regs. or is dangerous.So you think MI are wrong stating there should be a local douple pole isolator? Do you not fit isolators adjacent to showers, cookers, heaters boilers ect..
The regs are a minimum guidance, nothing stopping you going a step further to better the install.
Madness not to have one imo.
Have you carried out many eicrs? Why would you test L-L on a ring final? L&N -earth (with cpc connected to earth bar) is only required IR test imo on eicr.
No isolator atall on shower is a c2 for me its cowboyish, provides no local isolation & doesnt comply with MI.
MIs are guidance only, and don't have to be followed, especially when they are wrong.
Sorry to be blunt but EICR's require a considerable level of experience and knowledge, you do not seem to me to have the required knowledge to be advising the client on such matters. Seems to be a case of the blind leading the blind.
So you think MI are wrong stating there should be a local douple pole isolator?
So you will add a fixed appliance, on a dual RCD board with no DP isolation ..... So when the RCD starts tripping how are you going to isolate the fixed device so you can rule out in or out as the cause of the tripping?
You can't so I have too disagree with you
So should I conclude no reg; Therefore, common sense should prevail?
You are not going to find a Regulation requiring local DP or even SP isolation in domestic installations.Back to the matter in hand, I can't find anything in BYB or OSG.
But Electrician's Guide to The Building Regulations advises;
4.5 "Instantaneous water heaters (including showers) of rating exceeding 3 kW should be supplied by a separate circuit. Local isolation of water and electricity should be provided to facilitate maintenance"
So should I conclude no reg; Therefore, common sense should prevail?
That argument applies to every light fitting throughout the house. Are you implying all light switches should be double pole?