There’s no Regs stating showers or other household appliances should have local isolation.
However where local isolation is desired, it’s not much use if it’s not local.
 
MIs are guidance only, and don't have to be followed, especially when they are wrong.

So you think MI are wrong stating there should be a local douple pole isolator? Do you not fit isolators adjacent to showers, cookers, heaters boilers ect..
The regs are a minimum guidance, nothing stopping you going a step further to better the install.
Madness not to have one imo.
 
So you think MI are wrong stating there should be a local douple pole isolator? Do you not fit isolators adjacent to showers, cookers, heaters boilers ect..
The regs are a minimum guidance, nothing stopping you going a step further to better the install.
Madness not to have one imo.
It’s not so much that they are wrong (though sometimes they clearly are), as whether non-compliance with an MI is a non-compliance with the Regs. or is dangerous.
 
Have you carried out many eicrs? Why would you test L-L on a ring final? L&N -earth (with cpc connected to earth bar) is only required IR test imo on eicr.
No isolator atall on shower is a c2 for me its cowboyish, provides no local isolation & doesnt comply with MI.

C2 ????????????????????

And you ask if I have done many EICRs?
 
MIs are guidance only, and don't have to be followed, especially when they are wrong.

So you will add a fixed appliance, on a dual RCD board with no DP isolation ..... So when the RCD starts tripping how are you going to isolate the fixed device so you can rule out in or out as the cause of the tripping?

You can't so I have too disagree with you
 
Sorry to be blunt but EICR's require a considerable level of experience and knowledge, you do not seem to me to have the required knowledge to be advising the client on such matters. Seems to be a case of the blind leading the blind.

It's a simple question, I can't find a reg.
If you are so clever why not just say it's reg nnn.n.n or no such reg ?

"Wise men speak because they have something to say; Fools because they have to say something." Plato
 
So you think MI are wrong stating there should be a local douple pole isolator?

If it is implied that it is a reg then yes they are wrong. If it is said they advise it though not required by the regs that is another matter.
 
So you will add a fixed appliance, on a dual RCD board with no DP isolation ..... So when the RCD starts tripping how are you going to isolate the fixed device so you can rule out in or out as the cause of the tripping?

You can't so I have too disagree with you

That argument applies to every light fitting throughout the house. Are you implying all light switches should be double pole?
 
Back to the matter in hand, I can't find anything in BYB or OSG.
But Electrician's Guide to The Building Regulations advises;
4.5 "Instantaneous water heaters (including showers) of rating exceeding 3 kW should be supplied by a separate circuit. Local isolation of water and electricity should be provided to facilitate maintenance"
So should I conclude no reg; Therefore, common sense should prevail?
 
Not sure how many FCUs are not double pole?
The ones I use are, so it’s not a problem for me.
 
Back to the matter in hand, I can't find anything in BYB or OSG.
But Electrician's Guide to The Building Regulations advises;
4.5 "Instantaneous water heaters (including showers) of rating exceeding 3 kW should be supplied by a separate circuit. Local isolation of water and electricity should be provided to facilitate maintenance"
So should I conclude no reg; Therefore, common sense should prevail?
You are not going to find a Regulation requiring local DP or even SP isolation in domestic installations.
There may be some in regards to rotating machinery in workshops and factories, but I can’t be asked to look.
 