Might be worth getting the trusty clamp meter out and see what current is being pulled when switched on as an indication.
Meanwell are one of the best brands of LED drivers available. I've used a wide range of their product line over the years and never been disappointed. It would be dangerous to assume that you could get insight into the performance or specs of another brand by referring to the datasheet of the Meanwell equivalent, I can almost guarantee the other brand will fall short and often by a large distance.This is a data sheet for a Meanwell 200w LED driver which is a popular unit used by quite a number of manufacturers.
I would imagine characteristics are similar for other brands.
They suggest 4 units on a 6A type B or 6 units on a 6A type C
ELG-200-MEAN WELL Switching Power Supply Manufacturer - https://www.meanwell.com/webapp/product/search.aspx?prod=ELG-200
.Your trusty clamp meter probably won’t react in time to give you an accurate reading especially if it’s digital, the inrush current drawn only lasts for microsecondsMight be worth getting the trusty clamp meter out and see what current is being pulled when switched on as an indication.
I had that problem once, inrush, you mucky people, some will get the joke some wont, not going to explain.Update!!
It was definitely in rush current!
I have not experienced it being a problem before as I only do domestic and Type C breakers are rarely needed.
I had taken in to account VD, worked out what the Zs was likely to be and used 6mm SWA for the approx 100m run.
My Zs is 1.45ohms.
I am picking up a Type C 6A and 10A tomorrow and will try those, however I did have a 16A Type B and this is working fine. The max Zs for 16A Type B is 2.2 ohms so I have been saved.
I can run another circuit for the next 5 x 200W lights or I might find that a 20A type B works for all 10 lights as long as the Zs < 1.75ohms.
I'm embarrassed that I didn't factor inrush current in to my design, it's not acceptable to be acting reactively like this to a problem that should never have arisen!
One last question..
What is the relationship between Type B and Type C MCB's with regards inrush current? What I mean is if for example a 6A Type B could take perhaps 100A for 0.2s without tripping what would the equivalent be for a 6A Type C be? Is there some data sheets on this or some interesting reading somewhere?
ps.. these are the lights http://www.belllighting.co.uk/fittings/SkylineProLEDFloodlightsWallpacks
Apparently the inrush current is approx 75A.
Thanks Marvo.Just as a footnote, if you're planning to add more lights onto the same supply I'd suggest supplying them via a separate switch or timer or PIR or whatever switching system they're on, even if it works out more costly. That way they won't all switch simultaneously which would add to the inrush current issue.
Just saw some tumbleweed roll pastI had that problem once, inrush, you mucky people, some will get the joke some wont, not going to explain.