Steve93

-
Trainee
Eicr today had a 4mm T+E connected into the bottom of a main switch which went to a separate dB with 1 20amp rcbo. Then swa to a hot tub. That part is fine. What I’m unsure about is the reg I can say that the cables are not ok in the bottom of the main switch. The other dB is only about a ft away from the main one. What’s people’s thoughts on this? I know it’s rough as you like!!
 
I assume the OP is referring to a standard 100a MS in a DB with a busbar and N link in the bottom
If that is the case you must question whether this is a means of connection which is condoned by the consumer unit manufacturer. Are the conductors suitably sized to withstand fault and short circuit current.
 
If that is the case you must question whether this is a means of connection which is condoned by the consumer unit manufacturer. Are the conductors suitably sized to withstand fault and short circuit current.

Not using a type tested assembly as intended by the manufacturer.

C2, as it could cause poor connection and possible CU fire. Bit of a judgement call.
 
[QUOTE - So the 4mm is protected by the cut out fuse?]

For fault current yep but depends on what type supply

[QUOTE So by the cut out fuse then?
What other ocpd is there?]

What over current can the 4mm suffer when it can pull no more than 20 amp?
 
The problem is, you can't rely on the 20a rcbo to protect the 4mm. What I mean by this is, future alterations, who's to say someone won't split that 4mm and feed something another db etc. There is nothing to protect that 4mm from overload.

It's the same as having a 1.5mm t+e for a lighting circuit protected by a 45a but at fused down to 6a at the first luminaire.
 
A very poor installation but could be compliant if the connections are sound and the cable route to the 20A RCBO is suitable, then the RCBO can provide sufficient protection to be acceptable.
However there are a lot of caveats to the compliance so not generally a good idea.
PD after point of protection.jpg
 
you can't rely on the 20a rcbo to protect the 4mm. What I mean by this is, future alterations,

It is not necessary or possible to protect an installation against incorrect future modifications. All systems can be modified so that they become dangerous.

It's the same as having a 1.5mm t+e for a lighting circuit protected by a 45a but at fused down to 6a at the first luminaire.

Not quite the same. Top of head without checking the numbers, think the 1.0mm² CPC would not be protected against fault current by a 45A fuse, whereas I think the 4mm² is protected by the cutout as would be any other tails if the CPC is 4mm² too, but if it's T+E, would have to look it up, sounds doubtful as mentioned above.

But the crux is 433.2.2 which allows OPD to be located somewhere other than at the source of the circuit, so long as certain criteria are met to reduce the probability of a fault on the circuit up to where the OPD is. It may be the case there that those criteria are met, whereas I don't think they would be on your hypothetical lighting circuit.

E2A:
What do you mean by in the bottom of the main switch.
what goes into the top?

Agreed, we should refer to supply side and load side. Those of us who spend most of our time with TP+N DB's are used to putting the supply into the botttom of the switch.
 
Last edited:
Hi - in order to make use of 433.2.2 as they’ve done I think they need to install the cable with specific protection against impact (say in metal conduit). Which I’m guessing won’t have been done. Reg 433.2.2 refers us to 434 and then 434.2.1 (ii) .
 
Hi - in order to make use of 433.2.2 as they’ve done I think they need to install the cable with specific protection against impact (say in metal conduit). Which I’m guessing won’t have been done. Reg 433.2.2 refers us to 434 and then 434.2.1 (ii) .
That is not the case.
Generally tails are not contained in conduit, the mechanical protection is provided by the sheath.
Hence why we no longer allow unsheathed tails.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Steve93

Trainee
-
Joined
Location
Southampton

Thread Information

Title
4mm cable into the bottom of main switch.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
46
Unsolved
--

Advert

Thread statistics

Created
Steve93,
Last reply from
Deleted member 9648,
Replies
46
Views
5,542

Advert

Back
Top