The problem is, you can't rely on the 20a rcbo to protect the 4mm. What I mean by this is, future alterations, who's to say someone won't split that 4mm and feed something another db etc. There is nothing to protect that 4mm from overload.

It's the same as having a 1.5mm t+e for a lighting circuit protected by a 45a but at fused down to 6a at the first luminaire.
 
Under fault conditions what is the maximum current/time a 4mm t+e can withstand?
What size fuse is protecting the 4mm cable from L to N & L to E faults?
 
you can't rely on the 20a rcbo to protect the 4mm. What I mean by this is, future alterations,

It is not necessary or possible to protect an installation against incorrect future modifications. All systems can be modified so that they become dangerous.

It's the same as having a 1.5mm t+e for a lighting circuit protected by a 45a but at fused down to 6a at the first luminaire.

Not quite the same. Top of head without checking the numbers, think the 1.0mm² CPC would not be protected against fault current by a 45A fuse, whereas I think the 4mm² is protected by the cutout as would be any other tails if the CPC is 4mm² too, but if it's T+E, would have to look it up, sounds doubtful as mentioned above.

But the crux is 433.2.2 which allows OPD to be located somewhere other than at the source of the circuit, so long as certain criteria are met to reduce the probability of a fault on the circuit up to where the OPD is. It may be the case there that those criteria are met, whereas I don't think they would be on your hypothetical lighting circuit.

E2A:
What do you mean by in the bottom of the main switch.
what goes into the top?

Agreed, we should refer to supply side and load side. Those of us who spend most of our time with TP+N DB's are used to putting the supply into the botttom of the switch.
 
Last edited:
Hi - in order to make use of 433.2.2 as they’ve done I think they need to install the cable with specific protection against impact (say in metal conduit). Which I’m guessing won’t have been done. Reg 433.2.2 refers us to 434 and then 434.2.1 (ii) .
 
Hi - in order to make use of 433.2.2 as they’ve done I think they need to install the cable with specific protection against impact (say in metal conduit). Which I’m guessing won’t have been done. Reg 433.2.2 refers us to 434 and then 434.2.1 (ii) .
That is not the case.
Generally tails are not contained in conduit, the mechanical protection is provided by the sheath.
Hence why we no longer allow unsheathed tails.
 

Reply to 4mm cable into the bottom of main switch. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looking for a little advise as I’m not sure what’s happening So I’m looking at moving a two way light switch probably about 100cm away from its...
Replies
12
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
504
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock