Eicr today had a 4mm T+E connected into the bottom of a main switch which went to a separate dB with 1 20amp rcbo. Then swa to a hot tub. That part is fine. What I’m unsure about is the reg I can say that the cables are not ok in the bottom of the main switch. The other dB is only about a ft away from the main one. What’s people’s thoughts on this? I know it’s rough as you like!!
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below

Steve93

-
Trainee
  • Thread Starter Thread Starter
  • #3
What would you code it? If at all? It’s rough as but can’t find anything on it
 
D

Deleted member 9648

If the 4mm is securely terminated along with the busbar/neutral link then I cant see a non-compliance. You need to use your judgement on whether the termination is sound. The different size conductors in the terminal may not result in a sound connection
 
I assume the OP is referring to a standard 100a MS in a DB with a busbar and N link in the bottom
If that is the case you must question whether this is a means of connection which is condoned by the consumer unit manufacturer. Are the conductors suitably sized to withstand fault and short circuit current.
 

GBDamo

-
Supporter
If that is the case you must question whether this is a means of connection which is condoned by the consumer unit manufacturer. Are the conductors suitably sized to withstand fault and short circuit current.
Not using a type tested assembly as intended by the manufacturer.

C2, as it could cause poor connection and possible CU fire. Bit of a judgement call.
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to 4mm cable into the bottom of main switch. in the Electrical Forum area at ElectriciansForums.net

Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom