Steve93
Eicr today had a 4mm T+E connected into the bottom of a main switch which went to a separate dB with 1 20amp rcbo. Then swa to a hot tub. That part is fine. What I’m unsure about is the reg I can say that the cables are not ok in the bottom of the main switch. The other dB is only about a ft away from the main one. What’s people’s thoughts on this? I know it’s rough as you like!!
I assume the OP is referring to a standard 100a MS in a DB with a busbar and N link in the bottom
If that is the case you must question whether this is a means of connection which is condoned by the consumer unit manufacturer. Are the conductors suitably sized to withstand fault and short circuit current.
Not using a type tested assembly as intended by the manufacturer.
C2, as it could cause poor connection and possible CU fire. Bit of a judgement call.