Eicr today had a 4mm T+E connected into the bottom of a main switch which went to a separate dB with 1 20amp rcbo. Then swa to a hot tub. That part is fine. What I’m unsure about is the reg I can say that the cables are not ok in the bottom of the main switch. The other dB is only about a ft away from the main one. What’s people’s thoughts on this? I know it’s rough as you like!!
I assume the OP is referring to a standard 100a MS in a DB with a busbar and N link in the bottom
If that is the case you must question whether this is a means of connection which is condoned by the consumer unit manufacturer. Are the conductors suitably sized to withstand fault and short circuit current.
Not using a type tested assembly as intended by the manufacturer.
C2, as it could cause poor connection and possible CU fire. Bit of a judgement call.
[QUOTE - So the 4mm is protected by the cut out fuse?]
For fault current yep but depends on what type supply
[QUOTE So by the cut out fuse then?
What other ocpd is there?]
What over current can the 4mm suffer when it can pull no more than 20 amp?
Reply to 4mm cable into the bottom of main switch. in the UK Electrical Forum area at ElectriciansForums.net
Looking for a little advise as I’m not sure what’s happening So I’m looking at moving a two way light switch probably about 100cm away from its...
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...