H

Haworth

Evening all. I’m struggling al little bit; doing a light installation (extra outdoor light). Upon undoing existing fixing I found there’s no CPC. Seems no CPC on any of the lights (even though there’s an earth in the DB). So, how would I get my R1 and Rn readings? I’m proper stuck so any help or ‘talk throughs’ would be greatly received.
 
I assume you mean R1+R2, the purpose of which is to verify a satisfactory cpc is present. As above, you should not be altering or extending a circuit that will not comply and will be potentially unsafe
 
Your problems are the cpc of your new cable has no continuity to the main earth terminal. You are therefore not satisfying the requirements for ADS even if additional rcd protection is in place which it should be assuming this is domestic. Check first saves a whole load of grief later.
Are you 100% sure there are no cpcs present through the rest of the circuit, possible they have just been cut off.
 
Last edited:
I’m going
I would suggest thats referring to a pendant from a ceiling rose, or luminaire using said pendant.

All other wiring points require a cpc.
I’m going to explain fully to customer what needs to be done before anything moves forward. Appreciate all the advice; probably lose the job but at least I’ve not cut corners to make a buck.
 
Wiring is already in place, just very old with no CPC, so going to suggest a CPC install or rewire.
 
rewire your outside light from socket circiuit (or any circuit with a cpc) via a 5A FCU. bear in mind that you also need RCD protection for luminaiires as of 1st January.
 
I would suggest thats referring to a pendant from a ceiling rose, or luminaire using said pendant.

All other wiring points require a cpc.

Not saying you're wrong, but how did you draw that conclusion? The BBB does specifically mention pendant sets and batten lampholders in a number of places, but not in this instance.
 
The last sentence of 411.3.1.1 suggests otherwise for lamp holders without exposed conductive parts. However, you will need a CPC at the switch.
Whilst the Class II lampholder suspended from a Class II point wouldn't require one, there still has to be one at the Class II luminaire. It just means you don't need a three core flex into the lampholder.
 