Discuss Test results, lighting circuit in the UK Electrical Forum area at ElectriciansForums.net
Evening all. I’m struggling al little bit; doing a light installation (extra outdoor light). Upon undoing existing fixing I found there’s no CPC. Seems no CPC on any of the lights (even though there’s an earth in the DB). So, how would I get my R1 and Rn readings? I’m proper stuck so any help or ‘talk throughs’ would be greatly received.
Your problems are the cpc of your new cable has no continuity to the main earth terminal. You are therefore not satisfying the requirements for ADS even if additional rcd protection is in place which it should be assuming this is domestic. Check first saves a whole load of grief later.
Are you 100% sure there are no cpcs present through the rest of the circuit, possible they have just been cut off.
I’m going
I would suggest thats referring to a pendant from a ceiling rose, or luminaire using said pendant.
All other wiring points require a cpc.
I’m going to explain fully to customer what needs to be done before anything moves forward. Appreciate all the advice; probably lose the job but at least I’ve not cut corners to make a buck.
rewire your outside light from socket circiuit (or any circuit with a cpc) via a 5A FCU. bear in mind that you also need RCD protection for luminaiires as of 1st January.
Not saying you're wrong, but how did you draw that conclusion? The BBB does specifically mention pendant sets and batten lampholders in a number of places, but not in this instance.
The last sentence of 411.3.1.1 suggests otherwise for lamp holders without exposed conductive parts. However, you will need a CPC at the switch.
Whilst the Class II lampholder suspended from a Class II point wouldn't require one, there still has to be one at the Class II luminaire. It just means you don't need a three core flex into the lampholder.
Reply to Test results, lighting circuit in the UK Electrical Forum area at ElectriciansForums.net
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
I’m just finishing my L2 2365 at college in the evenings and plan to do the L3 2365 with the same college as an evening course. However I would...