Good Morning ALL
I have a terraced house and let out . Novice Landlard and come across to this site/ forum Many Thanks and informative,

have had two FI several C2 & C3 But no C1.

F1 as cause Meter tails are 16mm . this is the cables between the meter and the consumer box.
I also have two 16mm cables just before the meter reading and I understand that these are installed by the co supplying the power to property. both the metr and the consumer unit box are 6/9 inches apart. Located in cupboard inside as terraced house.

when questioned the Electric Engineers (EE) says that its not your lookout - Find it weird as he was on about safety of tenant etc. / insurances etc.

The report requires 25mm .

Another confusing issue is; Has given an overall summary 'UNSATISFACTORY' but than in recomendations in Sec 6 as has put subject to remedial action taken / Further Investigations tested in 3 years or change of tenancy.

Amother issue was the Consumer Box Changed by another EE 4 years ago and Building Regulations Certificate of Compliance held. This EE mentions that the consumer unit is a cheap version should be replace, though the Guy who did it 4 years ago is a listed and approved trader person with NICEIC

Questions:
1. Is this still safe for tenants to continue living there and remedial actions taken
2. what are your thoughts ?

Regards and many thanks
PK
 
A 'cheap' CU being flagged as a defect is a first for me and totally inadequate unless backed up by lack of BS compliance or a similar reason.
Reasons may include non amendment 3 compliance in an escape route, or non compatible components....but 'cheap'?? is that really how its worded?
 
I think a look at this report would help us give you a bit more info.
Can you post it here with personal details removed?
 
As James just said, post up the report on here with any personal details blacked out, and some pics would help to go with it. Something doesn't smell right here at all!
 
What are the C2s
Many Thanks all for your help.
I am aware that C2 needs to be addresses promptly . But was more concerned about the CU box which was installed 4 years ago and independently inspected.

C2 & C3 as attached pdf & so is F1 to make it easier.
All help greatly appreciated.
Regards
PK
 

Attachments

16mm tails ... no code unless signs of damage, thermal or physical. .what make is the CU, and list the C2's
Hi -

Defo no signs of damage on 16mm tails. - full report posted & no mention re damage.
Will post picture soon.
Thnx
 
some of those C2's are easily remedied. wonder why "LIM" on IR test voltage. the non fire rated downlight C2 is questionable. and the 16mm tails should be no code. has it really got a 3036 DNO fuse?
 
The DNO fuse is shown as 60 amp so 16mm tails are fine.

RCD failed to trip when tested is a C2.

TBH the inspector could have expanded on the other items rather than just copy and paste the regulation. Have they sent any pictures of the faults?
 