If he is intent on replacing this cable then do it temporarily first without destroying the wall and decoration.
Is it something that can be done temporarily?!If he is intent on replacing this cable then do it temporarily first without destroying the wall and decoration.
Hi Telectrix1. outside lights. both L and N need to be disconnected to rule them out.
2.Insulation testing should give high readings, in the MegOhm range, not 0 as your neighbour says.
3.this is not a job for a handman with a miltimeter. it requires an electrician experienced in fault finding with the correct tester/s to investigate.
4. rewiring a "suspect" cable can cause untold damage to decor and you may still have the fault after.
Quite! I just asked his wife and she said he did use an MFT but I've just googled and I don't think he did - I think he used a Fluke T6-1000, LCD Voltage tester.The plot thickens, you most definitely need a professional electrician to look at this, does you friend have home emergency insurance? if so call them out.
What is the ceiling construction if its a suspended ceiling then the temporary fix is a simple matter.
I know - I'm working on it. But in the meantime, could you give me a clue to number 1? Is what he did enough to 'disconnect' the outside lights, thus isolating them?re-read my point #3 in my last post. it's the only viable option.
no. as you could have a N-E fault which would still be there if you only disconnect L.I know - I'm working on it. But in the meantime, could you give me a clue to number 1? Is what he did enough to 'disconnect' the outside lights, thus isolating them?
Most like the one in the middle. I linked to what I think he used earlier, but it's perhaps under moderation still. My memory is it looks like the Fluke T6-1000, LCD Voltage tester, but I don't remember the pincer like top part.Which of these instruments he used did it look similar too.View attachment 63753
So disconnecting all the wires within the dimmer switches for the outside lights would suffice for full disconnection? I'll try that to see if that isolates it.no. as you could have a N-E fault which would still be there if you only disconnect L.
not necessarily. you maynot have the neutral at the switch.So disconnecting all the wires within the dimmer switches for the outside lights would suffice for full disconnection? I'll try that to see if that isolates it.