- Oct 13, 2019
- 191
- 57
- 103
- If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
- United Kingdom
- What type of forum member are you?
- Other
- If other, please explain
- Spouse of an advanced city and guilds electronics Lab technician (retired) and DIYer
Daughter’s new house.
Garage has very old wylex distribution box connected to a double socket and a lighting circuit with one neon.
put an RCD’ed extension cord in socket and the RCD trips instantly.
Measured leak current at main fuse area.
The neon light was switched off.
Leakages
house as is : 3.8 ma
House with garage distribution switched off 3.4 ma.
Using another circuit,extension cable 0ma
can use tools in socket without problem.
I think there is a fault in the distribution box in the garage.
seeking other opinions?
Garage has very old wylex distribution box connected to a double socket and a lighting circuit with one neon.
put an RCD’ed extension cord in socket and the RCD trips instantly.
Measured leak current at main fuse area.
The neon light was switched off.
Leakages
house as is : 3.8 ma
House with garage distribution switched off 3.4 ma.
Using another circuit,extension cable 0ma
can use tools in socket without problem.
I think there is a fault in the distribution box in the garage.
seeking other opinions?