Hi, I’m a bit new to this and I understand how to wire thru a grid key switch for emergency lighting but could someone please explain or show a small drawing how to wire with a key switch so when the key switch is toggled, the lights stay in and only turns off the emergency lights please
Just break the permanent or emergency feed through the key switch. The switch feed to the rest of the lights should be totally separate.
Anyone ever seen this done properly.. emg lights only controlled by key switch & not looped of in circuit with other ordinary lights
The way I seen them done is CTU and multipole n/c contactor in the DB
Each lighting MCB you take a feed through a pole for emergencies
Ctu breaks the poles
Interesting...
I am no expert on this, but in a recent installation of maintained units, a separate permanent live was installed, without key-switches. Thus, when doing monthly testing we just trip the breaker for the lights and check that the ones with emergency modules stay lit...which they do. We don't check for them staying on for 3 hours, but an hour is fine, as the building is small and can be evacuated in under 2 minutes via 3 exits. Probably not "best practice" but for a small building it works fine.
Interesting...
I don't get that?
Yes, that's pretty much it. Basically, a P/L which keeps the battery charged. However, should the RCBO trip, the emergency option is triggered, and the luminaire stays lit, on battery power. They have an LED on the frame which shows green when all is well and the battery is charging, and red when in emergency mode. Thus, when the luminaire is switched off, at the switch, the battery is still being kept on charge. Tripping the RCBO simulates a loss of power. That is how it is tested, instead of having a key switch in the circuit.
The top drawing is preferred as the test facility only isolates the permanent supply, the bottom drawing will also isolate the general lighting.
Is it the same lamp powered by the switched live as the battery
You turn off the switched live ,the lamp goes out and then the key switch brings it back on to prove the backup system ?
Led maintained bulkhead
What 50,000 hrs life ,low.wattage
Is there any need to be messing with switched lives ?
Keyswitch or rcbo as above and leave it on 24/7 I dunno ?