B
BrianHJR
Edited - please read right to the end!
Grateful for any advice regarding CT metering which seems to be generating inaccurate/implausible readings.
Our charity has a commercial building with 3-phase connection into a busbar chamber at one end - let’s call us ABC.
The rest of the chamber supplies three other switched fuses supplying another business nearby with 3 x single phase supplies - let’s call it XYZ.
The landlord had a contractor install 2 x Socomec Countis E42 units to meter our usage separately from the other business. They were set up so that XYZ meter records total usage, and ABC meter records only our usage.
Our ABC meter did not register any usage from day one, we let them know but they did nothing for months. Eventually they got the same contractors out to investigate and repair.
Since they did this our meter works, but the readings seem implausibly high, especially when compared to the XYZ usage.
Recently one of the directors observed that in 2.5 hours, our ABC meter incremented by 3KWH with just a few fluorescent light tubes on.
In the same time period, the business XYZ only had 1 KWH increment on their meter, despite being observed to have far more potential usage.
Does anyone have any experience of current transformers being inaccurate?
Could the issue be that we are using all 3 phases?
Might it just be a really bad or problematic install?
The landlord has tried to tell us it’s fine, but they did eventually say they’d get the contractors back out to have a look… we have considered installing our own check-meter but it’s a cost we really don’t need!
I’ve attached images of the install before the repair - I’ve no reason to believe they’ve changed the position of the CT clamps but I’ve not had a chance to look inside the bus bar chamber recently…
Our ABC connection is on the far right - the other 3 connections run to XYZ supplies…
Thanks in advance.
EDIT: Having thought about it a bit deeper, I’m pretty certain that they must have adjusted the positions of the CTs as the metering is now supposed to be completely separate… so the image will not be terribly useful in diagnosing the latest issues.
I’ll try to get an updated photo when I can… unfortunately it’s a two person job to remove the BBC cover since they mounted the meter box onto the front of it!
They have been installed incorrectly the CTs for your usage should be around the grey wires which supply the ABC switch. It is not a wise thing to be removing that busbar chamber cover, one false move and there will be a rather large BANG!
The XYZ switches are actually off?
There's various CT's available which have various numbers of windings. The meters need to be programmed to the type of CT that's been used. The CT ratio will be on the CT's label. This needs to match the setting in the meter. There's various other parameters that need to be set correctly. If you've got a clearer photo of the CT's for your supply, we might be able to identify it for you. If the meter isn't password protected you could then download the installation instructions and look at the settings to see if they're correct.
I wouldn't put them around the bars myself, but I think they are placed to collect the right consumption for unit ABC.
Cts look OK to me.
Agree totally regarding removing the covers!!
I think it is more likely that the ct ratio has been incorrectly set on the meter, or the ct secondary winding connections have been mixed up
EDIT: Considering there are no markings on the secondary cables, I wouldn't be surprised if the ct connections, or/and voltage connections have been connected incorrectly
Be extremely careful removing those covers if the instalation is not isolated.
I can’t tell if the ABC usage ct’s are in the right place, it depends on what else is on the right, out of the picture.
I appreciate the comments so far.
I’m going to get an updated picture when I’m able to be there when someone else is in.
The advice re removing the chamber cover is obviously well intentioned, but completely unnecessary - whenever we’ve accessed the interior, we’ve first thrown the main switch underneath…
That still isn't sufficient, there is a proper isolation procedure, just operating the switch, whilst it appears enough, it doesn't prove things are safe, only that they might be.
We isolate the main switch on the incomer to the building.
In what way is this insufficient?
Are you the only ones supplied from that busbar because the only other switch fuses in view are switched off.
Is it locked off to prevent any of the other users re-energising it while you have the cover off? If so how?
Yes.
It’s because I’d turned off all the outgoing switch fuses before operating the main incomer. Many years ago I was told that it‘s good practice to do so, not sure if that’s true but it’s habit now!
Thanks in advance.
View attachment 94006View attachment 94006
Are the CTs of the correct ratio and compatible with the meters???
Of course. We have a specific iso padlock for doing just that.
Moderately pointless though, because the main isolator is right underneath the bus bar and so anyone turning it back on would have had to fight their way past us first…
We don’t know. We aren’t going to mess with the meters because that would open us up to accusations of tampering…
I was posting on here to get some ideas of what might be wrong so that we can query this with the site management, who are otherwise pretty clueless.
In what way
Review the attached.
There is no guarantee that the switch operates and isolates correctly, therefore you must check before working on anything
I'd use similar logic with regards to locking off when I'm the only person in a building but, unlike cats, we only have one life and I'd prefer to go beyond reliance on a switch when ensuring isolation of supply.
Reactions: pc1966
Thanks in advance.
As already mentioned, check the CT ratio is correct. Verify they have not used protection type CTs by mistake as these are normally not suitable for metering!
And those secondary connections on the CTs need earthed as well for safety!
Reactions: BrianHJR
Provided there is nothing else to the right of your fused-switch then the CT location is correct, even if putting them on the busbars a bit off. However as already pointed you the meter has to be set with the correct ratio so you get charged for 1A * 230V and not 5A * 230V if the ratio is out by 5, etc.
The CT for the main supply looks odd, two of them seem to be on the incoming supply taps but 'blue' L3 is off the busbar as nothing to the left seems to use it.
Final question, how are the metering cables taking out with the cover on? Please tell me they are not crushed under the lid?!!! There is no adequate protective fusing of the voltage tap meter cables so they should be subject to additional protection against mechanical damage / shorting out / etc!
ccan't open it
ccan't open it
Oops
It's the best practice guide 2 from electrical safety first.
https://www.----------------------------/professional-resources/best-practice-guides/
Could no-one else open it? Works for me
Oops
Works OK for me as well.
Using Firefox on desktop so maybe not so good on mobile/tablet?
I’d certainly not trust the meter installers to have got it right. Neither of our NICEIC people thought very much of the install when they visited.
Yes that strikes odd, they have done it like that because there wasn’t enough space to clamp the grey phase incomer.
And you’re correct, XYZ only run on the brown and black phases.
The cables go through the front of the chamber and into the back of the meter box through a brass bush fortunately.
Very good point about the metering wires, they should presumably be insulated and sheathed like the rest of the cabling within the chamber?
I’ve attached a couple of photos of the inside of the meter box showing the wires supplying the power for the meters via an MCB - you can hopefully see that they have several cuts on them, fully down to the conductors - as left by the installers.
also a minor point but should the metal backplate in the meter box be bonded?
There‘s currently no proper bonding to the front cover of the bus bar chamber either, other than that tenuously provided by the fixing bolts…
So the electrical company were sent back to investigate the metering issues and fitted completely new ones in a different location, rather than bolting the meter box to the front of the bus bar chamber lid they have put it above on the wall.
The install seems to be of a significantly higher standard this time, but there is one potential glaring issue if we ever decide to use the spare switch fuse for anything else in future…
They didn’t leave any instructions for getting the meter readings and I had to work that out myself today.
A much better idea would have been for them to mount the metering box outside on the external wall, so that they wouldn’t have to rely on us for the figures and could send someone out to periodically check it?
The good news is that the meters are now producing plausible readings. The instantaneous import reading for our building showed a KW figure which was completely reasonable for the demand at that point and so we can hopefully now assume that the CTs are set up correctly…
I have encountered a similar problem recently, and I am trying to solve it,by some new devices,i hope these could help me solve my problems
Current transformer metering producing implausible readings
Commercial Electrical Advice
BrianHJR,
Heriberto Batchellor,