ccan't open it
Oops

It's the best practice guide 2 from electrical safety first.

Could no-one else open it? Works for me
 
Oops

It's the best practice guide 2 from electrical safety first.

Could no-one else open it? Works for me
Works OK for me as well.

Using Firefox on desktop so maybe not so good on mobile/tablet?
 
Review the attached.

There is no guarantee that the switch operates and isolates correctly, therefore you must check before working on anyth
Provided there is nothing else to the right of your fused-switch then the CT location is correct, even if putting them on the busbars a bit off. However as already pointed you the meter has to be set with the correct ratio so you get charged for 1A * 230V and not 5A * 230V if the ratio is out by 5, etc.
I’d certainly not trust the meter installers to have got it right. Neither of our NICEIC people thought very much of the install when they visited.

The CT for the main supply looks odd, two of them seem to be on the incoming supply taps but 'blue' L3 is off the busbar as nothing to the left seems to use it.
Yes that strikes odd, they have done it like that because there wasn’t enough space to clamp the grey phase incomer.
And you’re correct, XYZ only run on the brown and black phases.

Final question, how are the metering cables taking out with the cover on? Please tell me they are not crushed under the lid?!!! There is no adequate protective fusing of the voltage tap meter cables so they should be subject to additional protection against mechanical damage / shorting out / etc
The cables go through the front of the chamber and into the back of the meter box through a brass bush fortunately.

Very good point about the metering wires, they should presumably be insulated and sheathed like the rest of the cabling within the chamber?

I’ve attached a couple of photos of the inside of the meter box showing the wires supplying the power for the meters via an MCB - you can hopefully see that they have several cuts on them, fully down to the conductors - as left by the installers.
also a minor point but should the metal backplate in the meter box be bonded?
There‘s currently no proper bonding to the front cover of the bus bar chamber either, other than that tenuously provided by the fixing bolts…
😬

1566203C-5CB1-4514-995A-AA7ECFCFDE7A.jpeg85157796-0095-451D-9C1F-5444E759241A.jpeg
 
So the electrical company were sent back to investigate the metering issues and fitted completely new ones in a different location, rather than bolting the meter box to the front of the bus bar chamber lid they have put it above on the wall.
The install seems to be of a significantly higher standard this time, but there is one potential glaring issue if we ever decide to use the spare switch fuse for anything else in future…

DEEC1256-6470-4184-B2AA-E6D1F83EFC05.jpeg

They didn’t leave any instructions for getting the meter readings and I had to work that out myself today.
A much better idea would have been for them to mount the metering box outside on the external wall, so that they wouldn’t have to rely on us for the figures and could send someone out to periodically check it?

The good news is that the meters are now producing plausible readings. The instantaneous import reading for our building showed a KW figure which was completely reasonable for the demand at that point and so we can hopefully now assume that the CTs are set up correctly…
 

Reply to Current transformer metering producing implausible readings in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

We have a meter EDMI - ES30B fitted to our property. I understand from the fact sheet for the smart meter...
Replies
13
Views
1K
Good morning, I have a 3 phase supply into my workshop Hager dist board. I need to measure my usage for business accounts. My Electrician...
Replies
13
Views
2K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
692
We have two single phase heat pumps on two phases of a three phase supply the third phase has an immersion heater. The heat pumps are set up as...
Replies
4
Views
1K
Hi we have a split phase supply and had a EDMI ES-30B 3 phase meter fitted. Our readings are extraordinarily high. It is an old farmhouse but...
Replies
3
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock