I'm sure its only ever constructive criticism right Glen?
oh aye...
just thought it a bit disconcerting that this fella thought it was cosha to start altering the characteristics of a circuit...
without consulting BS7671, looking at the existing to verify or getting some values first to confirm what he was going to do was acceptable...
very strange...
Good day Guys
Read all the comments. Similar issue, I have a 32A MCB Hager NF332A for battery charger to charge Airplane Luggage Tuggers. Recently been tripping out a lot, measured and found 25A on each phase. Nothing has changed but the vendor purchased new units. so my calculation as per root3 method comes to18,475A max, which would explain the tripping. to fix this i would need a 43,3A minimum which i would need a 50A breaker. this really seems like too much and i am thinking we going to burn the cabling or connection points as they are all rated at 32A.
As per your guys comment the 32A should be sufficient to keep the 25A load, as is. Might be something else causing the trip?
So, your saying a three-phase circuit breaker say 32 amp is actually 3x32amp MCBs fitted together?
i am highly thinking this is the case. As per the OEM (Technical Properties NF332A - https://www.africa.hager.com/nf/products/energy-distribution/protection-devices/miniature-circuit-breakers/mcbs-ne-nf/nf332a/20543.htm) its rated at 32A not specifying whether its per phase or not. i do not think they will design a unit that first needs calculation to install. opens up for too many ways for error. so i am with you on this one. would of been great to hear from someone working at breaker OEMs
Good day Guys
32A should be correct for a 25A load .. might need a C type, dependent on Zs and disconnection times being met. also check that cable size is sufficient for 25A. installation ref. methods may lead to derating of the cable.
Yes it is. A C type breaker, will check Z,s n times
max. Zs for a 32A type C is 0.7 ohms.
ta-electrical,
telectrix,